Hey folks,
We run 4 Frame 6's (Mark VI - base load is around 37MW) with 2 steam turbines in an islanded grid with an overall power demand of about 250 MW. Each GTG / HRSG also has auxiliary firing. GTGs run in droop control. The auxiliary firing / steam is then adjusted to try & maintain the GTGs about 5-7MW below base load to avoid significant load shedding on trips. We assume that we have about 5MW IRM per machine typically hence the 5MW below base load. I am wondering whether it is feasible to run closer to base load to minimize emissions (reduce auxiliary firing) and rely on overload / peak load on the GTGs during trip events. We probably have about 10% extra capacity in terms of MW with peak load.
Any thoughts or suggestions on things to consider and whether this is even possible