Companion Guide to Ladder Logic / ST Conversion

This guide examines common ladder logic structures and presents the equivalent structured text representation, mainly intended as a learning guide for those getting started with ST.


Technical Article October 19, 2026 by David Peterson

Are you a seasoned ladder logic veteran, but brand-new to structured text? This guide compares most of the common ladder logic structures to their equivalent structured text format.

Not every ladder logic command is available in all IDEs, so the examples draw from multiple vendors. However, any IEC 61131-compliant structured text routine will accept the ST versions.

One note about tags in ST. Just like in any PLC program, variables can exist as global or local (program) tags. Tags are never declared right beside the ladder rungs, and likewise, variables are not declared right alongside the lines of code.

In the following examples, some snippets use variables beyond the I/O tags. They are listed as suggestions, but in real code, they will be declared as local (program) scope variables in the respective IDE, usually at the very beginning of each routine.

For all of these examples, InputTag is the real-world input terminal state, and OutputTag is directly sent to an output terminal. Assume they are already declared in the global tag/variable list.

 


Contacts and Coils


NO Contact (XIC):

OutputTag := InputTag;

 


NC Contact (XIO):

OutputTag := NOT InputTag;

 


Rising Edge (One-shot Rising):

VAR
   OldInput : BOOL := InputTag;
END_VAR

// Compare to see if it was 0 and is now 1
IF (NOT OldInput AND InputTag) THEN
  OutputTag := 1;
ELSE
  OutputTag := 0;
END_IF;

// Need to replace the old value so it can compare in the next scan cycle
OldInput := InputTag;

 


Falling Edge (One-shot Falling):

VAR
   OldInput : BOOL := InputTag;
END_VAR

// Compare to see if it was 1 and is now 0
IF (OldInput AND NOT InputTag) THEN
   OutputTag := 1;
ELSE
   OutputTag := 0;
END_IF;

// Need to replace the old value so it can compare in the next scan cycle
OldInput := InputTag;

 


Momentary Output Energize (OTE):

OutputTag := NOT EstopInputTag AND (InputTag OR OutputTag);

Note: If the E-stop is a normally closed device (as most are), then use a NO contact instruction in the ladder, or remove the ‘NOT’ term from the ST code.

 


Output Latch (OTL):

IF InputTag THEN
   OutputTag := 1;
END_IF;

//Remember to find another spot to turn it off

 


Output Unlatch (OTU):

IF InputTag THEN
   OutputTag := 0;
END_IF;

//Make sure there is another spot that turns it on

 


Toggle:

IF InputTag THEN
   OutputTag := NOT OutputTag;
END_IF;

//This happens continuously while the rung is true. Consider adding one-shot logic to toggle on each distinct input

 


Flasher:

VAR
   OnTime : TIME := Tx; // User input ON time, written with #ms, #s, #m, or #h suffix
   OffTime : TIME := Ty; // User input OFF time, written with #ms, #s, #m, or #h suffix
   InitOffTime : TIME := T0#ms; // Initially turns the output ON with no delay
   OldTime : TIME;
END_VAR

IF InputTag THEN
   IF OutputTag AND ((TIME() - OldTime)>=OnTime) THEN
      OutputTag := 0;
      OldTime := TIME();
   ELSIF NOT OutputTag AND ((TIME() - OldTime)>=InitOffTime) THEN
      OutputTag := 1;
      OldTime := TIME();
      InitOffTime := OffTime;
ELSE
   OutputTag := 0;
END_IF;

 


Math


Simple Comparison:

VAR
   Threshold : INT := x; // User input limit value
   Threshold2 : INT := y; // <u>Optional</u> second user input limit value
   Thresholdn : INT := n; // <u>Optional</u> all other user input limit values
END_VAR

IF InputTag > Threshold THEN
   OutputTag := 1;
ELSIF InputTag > Threshold2 THEN // Optional multiple thresholds, like a fill level with intervals
   MoreOutputTags := 1;
ELSE
   OutputTag := 0;
END_IF

 

All comparison operators are valid:

X Greater than Y X > Y
X Greater than or equal to Y X >= Y
X Less than Y X < Y
X Less than or equal to Y X <= Y
X Equal to Y X = Y
X Not equal to Y X <> Y

 


Comparison Limits:

VAR
   LowerThreshold : INT := x; // User input limit value
   UpperThreshold : INT := y; // User input limit value
END_VAR

IF InputTag >= LowerThreshold AND InputTag <= UpperThreshold THEN
   OutputTag := 1;
ELSE
   OutputTag := 0;
END_IF

 


Computation:

OutputTag := InputTag + 100;

 


Linear Scale:

As an example to help this make sense, assume you want to convert an input -10 to 10 V signal into its equivalent 4-20 mA signal. This uses the point-slope calculation of a linear equation.

$$ y = m(x-x_1)+y_1 $$

Where

$$ m = \frac{y_2-y_1}{x_2-x_1} $$

 

VAR
   LowerX : INT := A; // User provided lower input value (ex. -10)
   UpperX : INT := B; // User provided upper input value (ex. 10)
   LowerY : INT := C; // User provided lower output value (ex. 4)
   UpperY : INT := D; // User provided upper output value (ex. 20)
END_VAR

OutputTag := ((UpperY - LowerY)/(UpperX - LowerX))*(InputTag - LowerX) + LowerY;

 


Find Max or Min Value:

VAR
   MaxVal : INT := InputTag;
END_VAR

IF InputTag > MaxVal THEN
   MaxVal := InputTag;
END_IF

 

- OR -

 

VAR
   MinVal : INT := InputTag;
END_VAR

IF MinVal > InputTag THEN
   MinVal := InputTag;
END_IF

 


Counters and Timers

Both counters and timers are available as standard data types, accessed by function blocks in most IDEs.

Each example below will show two concepts:

  1. The standard function declaration and call.
  2. The code that explains the internal operation of the function, just for the love of the coding game.

Counter (Up Count):

VAR
   CounterName : CTU;
   PRE : DINT := x; // User supplied preset value
END_VAR

CounterName(CU := InputTag, RESET := ResetInput , PV := PRE);
OutputTag := CounterName.Q;

 

—----------------------

 

VAR
   ACC : DINT := 0;
   PRE : DINT := x; // User supplied preset value
   OldInput : BOOL := InputTag;
END_VAR

// Begins with a rising edge one-shot trigger
   IF (NOT OldInput AND InputTag) THEN
   ACC := ACC + 1;
END_IF;
OldInput := InputTag;

// OutputTag acts as IEC 61131 Q bit
IF ACC >= PRE THEN
   OutputTag := 1;
ELSE
   OutputTag := 0;
END_IF

IF ResetInput THEN
   ACC := 0;
END_IF

 


On-delay Timer (TON):

VAR
TimerName : TON;
   PRE : TIME := x; // User supplied preset value, written with #ms, #s, #m, or #h suffix
END_VAR

TimerName(IN := InputTag, PT := PRE);
OutputTag := TimerName.Q;

 

—----------------

 

VAR
   ACC : TIME := 0;
   StartTime : TIME := TIME();
   PRE : TIME := x; // User supplied preset value, written with ms, s, m, or h suffix
   OldInput : BOOL := InputTag;
END_VAR

// Start timer on rising edge of input tag
IF (NOT OldInput AND InputTag) THEN
   StartTime := TIME();
END_IF
OldInput := InputTag;

// Continue accumulating while button is pressed
IF InputTag THEN
   ACC := TIME() - StartTime;
ELSE
   ACC := 0; // If InputTag becomes false at any time, reset ACC
END_IF;

// In this routine, outputTag acts as IEC 61131 Q bit
IF ACC >= PRE THEN
   OutputTag := 1;
ELSE
   OutputTag := 0;
END_IF

 


Off-delay Timer (TOF):

VAR
   TimerName : TOF;
   PRE : TIME := x; // User supplied preset value, written with #ms, #s, #m, or #h suffix
END_VAR

TimerName(IN := InputTag, PT := PRE);
OutputTag := TimerName.Q;

 

—---------------

 

VAR
   ACC : TIME := 0;
   StartTime : TIME := TIME();
   PRE : TIME := x; // User supplied preset value, written with ms, s, m, or h suffix
   OldInput : BOOL := InputTag;
END_VAR

// Energize output (Q) on rising edge of input tag
IF (NOT OldInput AND InputTag) THEN
   OutputTag := 1;
END_IF

// Begin ACC time on falling edge of input tag
IF (OldInput AND NOT InputTag) THEN
   StartTime := TIME();
END_IF
OldInput := InputTag;

// Continue accumulating while button is pressed
IF InputTag THEN
   ACC := TIME() - StartTime;
END_IF;

// Reset output (Q) when time is reached
IF ACC >= PRE THEN
   OutputTag := 0;
END_IF

 

Fellow programming friends: if you notice any errors in these codes, please point them out so they can be corrected. I tried to keep them all accurate with the HTML formatting for the page, but please flag any errors or suggest alternatives to any of these routines - we appreciate the feedback!