Hi
Has anyone used the Sierra Tm100 Thermal Mass FT (4-wire)? I have one query regarding the 4-20mA connection. I followed the product manual for 4-20 mA termination, but still the transmitter is unable to transmit the 4-20 mA signal in SCADA (the loop was clear; no issue with the cable). From the attached drawing, is the manufacturer recommending using a 250-ohm resistor? But why does my control system have I/O (Siemens S-1500, AI Siemens ET200SP series) already loaded with resistance? I haven't seen it for Siemens Corilios FT, Yokogawa, Honeywell, or ABB. Is it recommended?
Has anyone used the Sierra Tm100 Thermal Mass FT (4-wire)? I have one query regarding the 4-20mA connection. I followed the product manual for 4-20 mA termination, but still the transmitter is unable to transmit the 4-20 mA signal in SCADA (the loop was clear; no issue with the cable). From the attached drawing, is the manufacturer recommending using a 250-ohm resistor? But why does my control system have I/O (Siemens S-1500, AI Siemens ET200SP series) already loaded with resistance? I haven't seen it for Siemens Corilios FT, Yokogawa, Honeywell, or ABB. Is it recommended?