Hi everyone,
I’m looking for some expert advice on a reactive load sharing and excitation issue we are experiencing with one of our marine generators.
System Setup:
• Application: Marine Genset (Caterpillar 3516B)
• AVR: Leroy-Somer R630
• PMS / Synchronization: SYMAP (running in Symmetric load sharing mode for both kW and kVAR).
• Busbar Voltage: 460V (60Hz)
Problem Description:
When this specific generator is synchronized and running in parallel with other gensets (ton the 460V busbar, it intermittently absorbs reactive power (negative kVAR / capacitive). Eventually, the SYMAP system trips the generator breaker, giving an "Excitation Fault" alarm (likely due to reverse kVAR / severe under-excitation). The issue is intermittent and usually happens when there are load fluctuations on the vessel.
Key Symptoms & Observations:
1. The Flashing LED: While running in parallel and taking negative kVAR, the pid iexc min LED on the R630 AVR flashes continuously.
2. Voltage Discrepancy: The main busbar operates at 460V. However, I noticed that the off-grid (no-load) voltage of this specific generator seems to be around 457V.
3. Hardware Condition: Because the pid iexc min LED is flashing, it indicates that the AVR is actively trying to reduce the excitation current to its absolute minimum limit. This leads me to believe that the rotating diodes, exciter, and main field are healthy, and the AVR is intentionally suppressing the field.
Current Hypothesis:
Because the generator's baseline voltage is set lower (457V) than the busbar (460V), the AVR "sees" the 460V upon synchronization as an overvoltage. It then aggressively reduces the excitation current to lower the voltage, hitting its minimum limit (iexc min). This intentional under-excitation causes the generator to absorb kVAR from the stronger generators on the bus, eventually leading to the SYMAP trip.
My Planned Action:
I am planning to take the generator off-grid (no-load) and adjust the baseline voltage to match the 460V busbar using the voltage setting potentiometer (P1/P5 depending on the exact R630 configuration), and slightly check the excitation ceiling limit (P4) to ensure it's not choking the AVR during high inductive demands.
Questions for the Experts:
1. Does my diagnosis regarding the pid iexc min flashing and the voltage discrepancy sound correct?
2. Are there any specific parameters or PID settings (like P7) on the R630, or within the SYMAP logic, that I should be double-checking before performing this mechanical adjustment?
3. Could there be any other hidden causes for this specific AVR behavior during parallel operation?
Note: the low KVAR on this generator was observed a long time ago but no trips happened, but during the past year we faced trips due to “Excitation fault” and no rewind nor any major maintenance were conducted.
Note 2: regarding adjusting AVR potentiometers, I would like to know which ones are to be adjusted when the generator on-load and parallel, and which ones are to be adjusted when generator is running off-load?
and which ones are NOT to be adjusted when generator is running in parallel?
Any insights or similar experiences would be highly appreciated.
Thanks in advance!


I’m looking for some expert advice on a reactive load sharing and excitation issue we are experiencing with one of our marine generators.
System Setup:
• Application: Marine Genset (Caterpillar 3516B)
• AVR: Leroy-Somer R630
• PMS / Synchronization: SYMAP (running in Symmetric load sharing mode for both kW and kVAR).
• Busbar Voltage: 460V (60Hz)
Problem Description:
When this specific generator is synchronized and running in parallel with other gensets (ton the 460V busbar, it intermittently absorbs reactive power (negative kVAR / capacitive). Eventually, the SYMAP system trips the generator breaker, giving an "Excitation Fault" alarm (likely due to reverse kVAR / severe under-excitation). The issue is intermittent and usually happens when there are load fluctuations on the vessel.
Key Symptoms & Observations:
1. The Flashing LED: While running in parallel and taking negative kVAR, the pid iexc min LED on the R630 AVR flashes continuously.
2. Voltage Discrepancy: The main busbar operates at 460V. However, I noticed that the off-grid (no-load) voltage of this specific generator seems to be around 457V.
3. Hardware Condition: Because the pid iexc min LED is flashing, it indicates that the AVR is actively trying to reduce the excitation current to its absolute minimum limit. This leads me to believe that the rotating diodes, exciter, and main field are healthy, and the AVR is intentionally suppressing the field.
Current Hypothesis:
Because the generator's baseline voltage is set lower (457V) than the busbar (460V), the AVR "sees" the 460V upon synchronization as an overvoltage. It then aggressively reduces the excitation current to lower the voltage, hitting its minimum limit (iexc min). This intentional under-excitation causes the generator to absorb kVAR from the stronger generators on the bus, eventually leading to the SYMAP trip.
My Planned Action:
I am planning to take the generator off-grid (no-load) and adjust the baseline voltage to match the 460V busbar using the voltage setting potentiometer (P1/P5 depending on the exact R630 configuration), and slightly check the excitation ceiling limit (P4) to ensure it's not choking the AVR during high inductive demands.
Questions for the Experts:
1. Does my diagnosis regarding the pid iexc min flashing and the voltage discrepancy sound correct?
2. Are there any specific parameters or PID settings (like P7) on the R630, or within the SYMAP logic, that I should be double-checking before performing this mechanical adjustment?
3. Could there be any other hidden causes for this specific AVR behavior during parallel operation?
Note: the low KVAR on this generator was observed a long time ago but no trips happened, but during the past year we faced trips due to “Excitation fault” and no rewind nor any major maintenance were conducted.
Note 2: regarding adjusting AVR potentiometers, I would like to know which ones are to be adjusted when the generator on-load and parallel, and which ones are to be adjusted when generator is running off-load?
and which ones are NOT to be adjusted when generator is running in parallel?
Any insights or similar experiences would be highly appreciated.
Thanks in advance!