Vacuum pressure is -160 mmH2O and we try to adjust but not affected, while other units vacuum pressure around -75 mmH2O.What's the vacuum on it?
Thank you for your valuable reply.@Rova,
I'm presuming you are referring to the L.O. Tank vacuum--and the main L.O. Mist Eliminator. Some machines with air-cooled generators have a separate L.O. Mist Eliminator for the generator bearing cavities/drains, and sometimes these have been known to have excessive vapor discharge, also. We don't know anything about the machines at your site (age of installation/commissioning; what maintenance outage was just completed and what work was done on the L.O. Mist Eliminator (if any). We don't know anything at all about the machine--except it's a Frame 9E GE-design heavy duty gas turbine, most likely driving a generator. The more information you can provide in your original post the more likely you will receive a more concise reply about the cause(s) of the problem.
NOTE: The purpose of all the questions below is to discuss most of the possible causes that have happened over decades at other sites. Since we didn't get a lot of information about the machine and the recent maintenance outage (completed by GE...) all we can do is try to ask questions and hope that one or more of them weren't considered and may help you to find and resolve the problem(s) (there may even be multiple issues contributing to this problem). Again, the more information you can provide the better the responses you will receive. EVERY TIME. GUARANTEED. As you can see, even with something as simple as the L.O. Mist Eliminator there are multiple conditions--none of which are controlled (typically) by the Mark* turbine control system and require manual inspection and verification during reassembly and if necessary after reassembly to eliminate them as a source of the problem or to find and resolve them when found to be incorrect. So, please don't be offended by the questions--we need more information to be of better help. AND, when you find and resolve the problem please write back to let others know what you found and how you resolved the problem. (A LOT of people read these threads--not just now, but in the future, also....)
Usually there is a NOTE on the L.O. system P&ID that specifies the vacuum to be present at the L.O. tank and at what load that vacuum should be present. What does your L.O. System P&ID say about the specified vacuum at the L.O. tank and when that measurement should be taken?
Please explain how you tried to adjust the vacuum on the L.O. tank.
Is there a pressure transducer providing the L.O. tank vacuum reading? Or is this reading coming from a gauge somewhere? If it's coming from a gauge, when (at what load) was this vacuum reading measured?
Is the gauge or pressure transducer a zero-centered device (meaning it shows or registers both pressure and vacuum? Was this device being used to measure L.O. tank vacuum "calibrated" during the maintenance outage?
What is the vacuum reading of the L.O. Tank when the machine is running at FSNL? What is the vapor discharge situation from the discharge of the L.O. Mist Eliminator at FSNL?
What is the vacuum reading of the L.O. Tank when the machine is running at 50% load? What is the vapor discharge situation from the discharge of the L.O. Mist Eliminator at 50% load?
What is the vacuum reading of the L.O. Tank when the machine is running at Base Load? What is the vapor discharge situation from the discharge of the L.O. Mist Eliminator at Base Load?
(In other words does the vacuum change when the load changes? And, does the amount of vapor discharge from the L.O. Mist Eliminator change when the load changes?)
When (at what load) were the other units' vacuum readings taken? Was an adjustment made to the as-found calibration adjustment of the device when the operation of the device was being "calibrated"?
There could be a problem with the assembly of the #2 Bearing Vent line after the maintenance outage. There could be too much pressure on the L.O. tank because of a misplaced or missing orifice in a Cooling & Sealing Air system line, probably suppling air to one of the turbine bearings.
There is supposed to a loop-seal drain between the bottom of the L.O. Mist Eliminator that is filled with oil to provide a seal between the L.O. Mist Eliminator vessel and the L.O. tank (where the condensed oil vapors are drained to). There is (or should be) a sight glass in this loop seal drain to prove there is oil in the piping of the loop seal.)
If the internal elements of the L.O. Mist Eliminator were not installed properly that could be a reason for excessive vapors discharging from the L.O. Mist Eliminator.
Sometimes, even when the proper vacuum at the L.O. tank is present at the specified load when the machine is running at low load or FSNL (Full Speed-No Load) the vacuum at the L.O. tank will be higher than at a much higher load and that can lead to issues with excessive vapors discharging from the L.O. Mist Eliminator.
That's a LOT of possibilities--and all of them have occurred at one time or another at most sites. A common reason sometimes is that manual valves were moved during the maintenance outage and not returned to the normal running position(s) prior to the re-start of the machine. Also, calibration errors can cause improper readings. Review BOTH the L.O. system and Cooling & Sealing Air system P&IDs to look for information about required vacuum readings, and orifice sizes. It may be necessary to shut the machine down to check the orifice sizes to be sure they were installed and sized correctly after the reassembly. And, at the same time, check the internal element arrangement of the L.O. Mist Eliminator to be sure everything is correct, and there is oil present in the loop seal between the L.O. Mist Eliminator and L.O. tank.
Best of luck; if you want more help--remember, we need more information.
| Thread starter | Similar threads | Forum | Replies | Date |
|---|---|---|---|---|
| K | Mist Eliminator Failure | Power Generation | 3 | |
| M | Oil Mist Eliminator Fan Motor Replacement | Power Generation | 1 | |
| S | Fumes from Lube Oil Tank Mist Eliminator Vent | Power Generation | 10 | |
| H | Heavy Mist/oil leaking from GE frame 9 mist Eliminator | Power Generation | 8 | |
| N | LUBE OIL MIST ELIMINATOR CHECK VALVE VCK20-13 AT GE 9e | Power Generation | 7 |