S
Tr-electronic absolute encoder
L2DP profibus communication
S5 plc-im308 module used for comm.
class2, scalling enable,
most signi.bit=25 forced to 1
type: CE100M, article nr:100-01102, maxppr 4096, max rotations 4096, version:Zn00-000-1170/v001, comm:RS485
we are using function block to read and write absolute encoder values. due to equipment failure reasons, i would like to preset new values from plc. but not getting preset. as per manufacturer inst, tried all the possiblities.
encoder connected for shear and used to take one rotation 360 degs. i would like to preset value which shear pos is not matching with actual.
i have tried all the possiblities and pl help me to overcome from this problem. same encoder used fixed with another machine and getting preset preset value ie 0.
please advice me and thanks for valuble reply and spending ur time for me.
regards
sankar
L2DP profibus communication
S5 plc-im308 module used for comm.
class2, scalling enable,
most signi.bit=25 forced to 1
type: CE100M, article nr:100-01102, maxppr 4096, max rotations 4096, version:Zn00-000-1170/v001, comm:RS485
we are using function block to read and write absolute encoder values. due to equipment failure reasons, i would like to preset new values from plc. but not getting preset. as per manufacturer inst, tried all the possiblities.
encoder connected for shear and used to take one rotation 360 degs. i would like to preset value which shear pos is not matching with actual.
i have tried all the possiblities and pl help me to overcome from this problem. same encoder used fixed with another machine and getting preset preset value ie 0.
please advice me and thanks for valuble reply and spending ur time for me.
regards
sankar