I am working on a GE 7FA MKV and I would like to add L62ES (Emergency Seal Oil Pump Start Timer) to the Timers and Counters. I have attached my TOTT_Q.SRC file below.
Please give me some detailed instructions on how to add L62ES as a timer to the totalizer without losing the timers and counters values. I should be able to map this signal to the HMI on the timers and counters screen using CIMPLICITY once it is properly configured. Thanks!
Anthony63
;---------------------------------------------------------------------
; Specify 1,2,3, or 4.
; types 1 (=counter)
; 2 (=timer)
; 3 (=analog accumulator)
; 4 (=accumulated logic) ;adds a constant value to an accumulator when
; pickup of a trigger logic is detected.
; Must keep signals in order.
;
; Signal Trigger level for
;Type Name analog type (opt)
;---- ------------ -----------------
;
1 L30CMIS
1 L30CTS
1 L30CFLS
1 L30CFS
1 L30CES
1 L30NA
2 LFALSE
1 L30NB
1 L30NP
1 L30ATS
1 LFALSE
2 L30FT_T
2 L30FT_P
2 L30FT_G
2 L30FT_L
2 LFALSE
2 L30FT_M1
2 L30FT_M2
2 L30FT_M3
2 L30FT_M4
2 L30FT_M5
2 L30FT_M5Q
2 L30FT_M6
2 L30FT_M6Q
Please give me some detailed instructions on how to add L62ES as a timer to the totalizer without losing the timers and counters values. I should be able to map this signal to the HMI on the timers and counters screen using CIMPLICITY once it is properly configured. Thanks!
Anthony63
;---------------------------------------------------------------------
; Specify 1,2,3, or 4.
; types 1 (=counter)
; 2 (=timer)
; 3 (=analog accumulator)
; 4 (=accumulated logic) ;adds a constant value to an accumulator when
; pickup of a trigger logic is detected.
; Must keep signals in order.
;
; Signal Trigger level for
;Type Name analog type (opt)
;---- ------------ -----------------
;
1 L30CMIS
1 L30CTS
1 L30CFLS
1 L30CFS
1 L30CES
1 L30NA
2 LFALSE
1 L30NB
1 L30NP
1 L30ATS
1 LFALSE
2 L30FT_T
2 L30FT_P
2 L30FT_G
2 L30FT_L
2 LFALSE
2 L30FT_M1
2 L30FT_M2
2 L30FT_M3
2 L30FT_M4
2 L30FT_M5
2 L30FT_M5Q
2 L30FT_M6
2 L30FT_M6Q