Crystal Clear CSAamit0612,
While a sizable portion of original posters to this site provide feedback on their issues, a larger number do not. Many are just hoping for an exact answer to their problem so they can go back to whatever they do when they are getting paid to troubleshoot problems or operate power generation equipment. I subscribe to the theory of, "If you give a man a fish you feed him for a day; if you teach him to fish you feed him for life." In other words, I'm trying to use some of these questions as a teaching tool to teach people how power generation works so that they become better at their jobs since so many people don't have or don't receive much, if any, training in power generation fundamentals or principles.
Good on you, mate, for using the 'Search' feature of Control.com (I'm presuming you used the 'Search' feature; I hope you used the 'Search' feature!). And, I hope you're looking for some basic operational and fundamental information as you try to solve your problem; it comes with the response--free of charge!
What part of:
"So, when a generator--and its prime mover--are tripped by reverse power that means the prime mover is not providing or producing sufficient torque to keep its generator spinning at its rated speed and the other generators it is synchronized tothe gridwill provide amperes to the generator, causing it to act like a motor, and spin the prime mover.
You need to understand why the prime mover isn't producing sufficient torque to keep the generator spinning at its rated speed."
didn't you understand?
Are you operating or troubleshooting a diesel gen-set? If not, what is the prime mover--a steam turbine? A gasoline engine? A hydro turbine? A combustion turbine?
If you have a diesel gen-set, then it's not getting enough fuel for some reason. If the load is dropping before the reverse power trip then the problem is likely dirty fuel filters or low fuel level or some kind of mechanical problem with the fuel rack slipping.
If the diesel control gets signals from another, external control system, the external control system might be not working properly. Or the wiring between the gen-set and the external control system might be bad.
When you want help with a problem, you need to provide more details than, "Help; it keeps tripping on reverse power." Here are a few ideas if you really want help:
What is going on when it trips?
Is there a large load change in the facility the gen-set is powering? (It's presumed the gen-set is powering some facility/load which is not being powered by a large grid/utility at the time of the reverse power tripping; if that's not correct, please tell us.)
Is the frequency of the system going high before the reverse power trip? (Or is the frequency going low?)
What mode is the diesel controller operating in: Droop or Isochronous speed control?
How many other gen-sets is the diesel synchronized with? (It's presumed the gen-set with the reverse power tripping problem is NOT synchronized to a large, "infinite" grid; if that's not correct, please tell us if it is.)
Are the other gen-sets significantly larger than the one that's having problems (higher rated power)?
What is the setting of the reverse power relay on the gen-set that keeps tripping?
Help us to help you!