Cimplicity & DCS System

N

Thread Starter

nour02525

We have a GE Gas turbine (mark VI control) and DCS is Ovation, the connection via GSM. but our GE HMI Server fail, and re-install again and now working in good way. but still GSM connection not working.
What is the steps and setting in Cimproject should to do to make connection available between GE and Ovation?

Thanks
 
You're going to have to provide some detailed information about the "failure" of the GE HMI Server (what failed), and what was done involving the "re-install" (was it done from a known good image of a working GE HMI Server created using the image utility provided by GE (usually Acronis); or was it done from the original back-up disks inside the CPU case--which are only there as a last resort, since proper images created using Acronis would be the preferred method of restoration)?

GSM is not usually a CIMPLICITY function; it's usually a TCI function. There may be some configuration information in the MS-Windows TCI Control Panel applet, or it may be found in CONFIG.DAT (wherever they put that file on your HMI--the location of some files seems to move around these days....).

But, you're going to need to provide more information about the failure and exactly how you "recovered" from it for anyone to be of more help.
 
thank you for reply.

the failure of GE HMI server is hard disk damage, and recovery through the restore initial image.

I check the CONFIG.dat file and found GSM is activate

GSM=yes
 
Top