Communicating between Allen Bradley to GE Fanuc PLC

S

Thread Starter

Sapan Kothari

Dear Sir,

We have to communicate AB PLC Micrologix-1200 with GE Fanuc PLC PCM Module - IC693CMM321.

We require RS485 communication from Micrologix-1200. Pls. send solution for the same.

If we use PM02 Cable, One sided D type connector shall be connected in Micrologix-1200 & other side shall be connected with ADAM (RS232 to RS485) convertor.

We will use this RS 485. Kindly Reply me on my mail id:
sapan.kothari [at] advancedsystek.com

Thanks & Regards,
Sapan Kothari,
Engineer - Projects,
M/s. Advanced Systek Pvt. Ltd.,
Vadodara, Gujarat,
India
 
D
The Micrologix supports Modbus on it's serial port....does the Fanuc unit? If so, that seems the most reasonable way to do so.
 
D
The GE Fanuc IC693CMM321 is an Ethernet module. It communicates using GE Fanuc's SRTP protocol OR Modbus TCP/IP. With Modbus TCP/IP it can be both a server and a client. Client requires programming using COMMREQ commands. Server requires no programming. However, as a server, the Modbus map for registers is non-standard. Access this link to download the Technical Manual for the IC693CMM321:
http://support.gefanuc.com/support/index?page=docchannel&id=09237d4900112007ff7cf003ad0

My suggestion would be to use Modbus TCP/IP between the two PLCs.

Drake Fink
Sr Application Engineer
GE Fanuc Intelligent Platforms, Inc.
 
J

Jerry Miille

Based on Mr. Fink's response earlier, you could consider our Omnii-Comm product http://www.miille.com/266-P00-Ethernet.pdf as a solution for a connection between Allen-Bradley PLCs and GE PLCs. We support both Modbus/TCP and Ethernet/IP at the same time. We are a "server" to both protocols. We can be a client for Ethernet/IP communication in some applications. You can contact me at jmiille [at] miille.com for more information.

Thanks,
Jerry Miille
 