We have a Series 4 Compressor Control system (CCC). The system icludes AntiSurge Control, Performance, and Speed Control Applications. Each application has its own duplex IOM cards. The system is 6 years old and has been a maintenance nightmare since day one. The system is interfaced with the DCS via a Modbus Link. The troubles that we've faced already include the following :
1) Fatal failures of IOM cards which requires replacing them with another new expensive card. The manufacturer never provided a conviencing reasoning behind these Fatal Failures.
2) Vague System alarms that come up every once in a while causing the cards sometimes to switcover to its backups. These alarms are not even explained in the literature, or explained in a line or two that doesnt lead to anything. Apparently, it was meant to be that way to call for CCC service whenever it has a hiccup.
3) Meaningless Common alarms get sent to the DCS which sometimes causes the boardman to ignore real critical alarms.
4) Complicated sequencing of Steam Turbine Startups with alot of irrelvant steps and safeguards.
5) Very Poor seequence of events and history to be used for trip investigations.
6) The software Platform is full of bugs and not user-friendly.
Does anyone else have a similar experience, and what would be an efficent solution to replace this system?
Thank you all.
Thank you all.