Yup. Go into RSLogix Help and look at the "Using the WALLCLOCK object" entry.
SLC and PLC users are used to having a bunch of system data arrayed in the "S:xx" status file. In the Logix family, you access things like the
wallclock or fault registers by executing a "Get System Variable" or "Set System Variable" instruction.
A few of these system variables are provided as internal tags, like the "S:FS" first-scan bit.
Cheers,
Ken Roach
A-B Seattle
>> Does the RSLogix 5k have internal timing tags such as 1 sec., 1 min., 1
>> hr. available ?
You have to use the instruction GSV get system variable in the class name put WALLCLOCKTIME
attribute name DateTime
at the destination you create a tag , you can name it what you want,. but the dimension must be at least 7 long