Equipment -
Motor 10 HP 480V 3 phase
Emerson Commander SK (brand new)
Motor was checked out by a rebuilder after it started tripping out the old drive and / or breaker.
No issues found except worn bearing seats which were re-machined.
Looked like the old Hitachi drive was history so a Emerson was purchased. Installed and programmed - try to start drive and instant DC bus overvoltage faults.
Disconnect motor and drive "runs" flawlessly.
Wired motor direct runs great with 7.6 / 7.8 / 6.9 amp readings. (fla is 13.3)
Voltages are 483 / 487 / 484.......
Any ideas ???