We have Alternator 15 MW, 5500 Volt, with field Excitation 12 Volt and 30 Amp. are it possible and safe, we change field winding for 70 Volt? this time no load Voltage are 4.0 volt and 8 Amp. span is minimum.
Ali... I don't believe that rewinding just the field-coil will work because the smaller wire-size will not fill-out the slot, thus affecting air-gap flux density!
Ali... unless the new conductor "area" is nearly equal to the original the solution proposed will not work! There are three reasons:
1) Current Flow
Current, not Volt Amperes, flowing through a conductor in a slot produces magneto-motive-force or mmf. Because your proposal produces less current, mmf will not be sufficient.
2) Flux Distribution
A rule for good design is that conductor-area should fill slot-area. Thus, flux distribution concentrates in the iron adjacent to the conductor. Unfortunately, in your proposal, this rule is negated. The smaller-size conductor will occupy about 17% of the original design. This causes flux-distribution to divide; one part in proximity to the conductor, the other in the slot space not occupied by the conductor. And, it does not matter whether the new conductor-area is located at the bottom of the slot or near the top!
3) Fill-in Material
What are you proposing? How will it be retained?