I am working on the RFG flow meter 51FT7133.
Originally the D/P flow transmitter was set to the manufacturer default of 210kpa.
Based upon the provided flow calculation (attached) we changed the flow meter calibration to 75Kpa (no square root extraction implemented in the transmitter).
The Mark VI Analog input for this instrument was originally set to 0-101 PSI, we have changed the analog input to 0-10.8778 PSIG corresponding to the calculation sheet. The temperature signal was 0-212F, we changed this to 32-212F to correspond with the field instrument range of 0-100c.
This D/P signal then feeds into a “mass flow” block within Mark VI with inputs from the static pressure and temperature transmitters and a constant.
When we simulated process values as per the supplied calculation sheet (D/P = 75Kpa, Pressure 20 BAR, Temperature 60c) the mass flow output on the Mark VI graphic (and our DCS) showed a flow of about 3600 KG/HR rather than the expected 8132 KG/HR.
Can this please be quantified, are we doing something wrong?
Because we are using the DCS flow for the control on a Fuel Gas heater system the figures are not only important for the operation of the GT.
A prompt reply would be appreciated.
Originally the D/P flow transmitter was set to the manufacturer default of 210kpa.
Based upon the provided flow calculation (attached) we changed the flow meter calibration to 75Kpa (no square root extraction implemented in the transmitter).
The Mark VI Analog input for this instrument was originally set to 0-101 PSI, we have changed the analog input to 0-10.8778 PSIG corresponding to the calculation sheet. The temperature signal was 0-212F, we changed this to 32-212F to correspond with the field instrument range of 0-100c.
This D/P signal then feeds into a “mass flow” block within Mark VI with inputs from the static pressure and temperature transmitters and a constant.
When we simulated process values as per the supplied calculation sheet (D/P = 75Kpa, Pressure 20 BAR, Temperature 60c) the mass flow output on the Mark VI graphic (and our DCS) showed a flow of about 3600 KG/HR rather than the expected 8132 KG/HR.
Can this please be quantified, are we doing something wrong?
Because we are using the DCS flow for the control on a Fuel Gas heater system the figures are not only important for the operation of the GT.