I have a problem with a differential transmitter DPT (measurement of LPG flow by a flat orifice of the Column to storage through pumps) which transmits the measurement to the regulator on DCS as shown in the diagram.
The problem is that the PDT does not follow the setpoint (Manual or Auto). the valve closed and the flow rate remains displayed, once 10t/h or more. If I open the valve for example: 40%, the flow rate indicates more than 70℅.
I did the calibration of the PDT on site and we coordinated with the flow rate indication on DCS. I adjusted it precisely. and once it was placed, the problem persists.
I tried to isolate the Auto valve completely, but the flow rate remains indicated 5 or 6t/h !!
knowing that:
Pdt scale: 0 to 2500mmH2O
Regulator tag: FIC4204 from 0 to 100t/h (see diagram).
Valve tag: FV4204.
The problem is that the PDT does not follow the setpoint (Manual or Auto). the valve closed and the flow rate remains displayed, once 10t/h or more. If I open the valve for example: 40%, the flow rate indicates more than 70℅.
I did the calibration of the PDT on site and we coordinated with the flow rate indication on DCS. I adjusted it precisely. and once it was placed, the problem persists.
I tried to isolate the Auto valve completely, but the flow rate remains indicated 5 or 6t/h !!
knowing that:
Pdt scale: 0 to 2500mmH2O
Regulator tag: FIC4204 from 0 to 100t/h (see diagram).
Valve tag: FV4204.