Hello,
In the summer 2024 our 7F gas turbine hydrogen cool generator (7FH2) had oil leak into the generator. We estimated about 200-300 gallons of lube oil leaked into the generator. We tried to drain out the oil at low point drain line but believe some oil might migrate into the stator or rotor also.
We also removed the coolers and clean them during an outage.
We did not note any issues during a normal running condition (100mw - 150mw(baseload)). However, at the summer VAR testing per NERC FAC-008 in June 2025, we received an alarm volt per hertz, which was a new alarm. The requirement of this test is to increase mvar until the unit power factor reaching +0.85 pf, at about +0.865 this volt/hertz alarm came in.
My Question is, could the lube oil in the generator cause this alarm?
Our next major outage will be in 2028, and would like to know if any other plant had the same problem and experienced any issues.
Thank you
In the summer 2024 our 7F gas turbine hydrogen cool generator (7FH2) had oil leak into the generator. We estimated about 200-300 gallons of lube oil leaked into the generator. We tried to drain out the oil at low point drain line but believe some oil might migrate into the stator or rotor also.
We also removed the coolers and clean them during an outage.
We did not note any issues during a normal running condition (100mw - 150mw(baseload)). However, at the summer VAR testing per NERC FAC-008 in June 2025, we received an alarm volt per hertz, which was a new alarm. The requirement of this test is to increase mvar until the unit power factor reaching +0.85 pf, at about +0.865 this volt/hertz alarm came in.
My Question is, could the lube oil in the generator cause this alarm?
Our next major outage will be in 2028, and would like to know if any other plant had the same problem and experienced any issues.
Thank you