Dear CSA and all,
This is my first post in this wonderful website, as I was only a reader since a long time ago.
In my plant we have 4 GE 5002D Gas Turbine which is a 2 shaft mechanical drive machine in a combined cycle application. originally the combustion system was a DLN system but 3 years back we did a retrofit to LHE combustion system. We experienced different flame counts on different machines.
2 months ago we had a flame out trip on machine (T4). we were suspecting the flame detectors to be the problem and we did replace 3 out 4 scanners and restart the machine. the situation improved since most of the readings went above 100 while they were around 55 to 80. Then, 2 weeks after the forth scanners reading dropped down to 50. We are investigating why we have low flame detectors reading on the fourth machine (T4)? That is reading lower counts than other machines, here are the current readings:
Can#11 is currently very low 50
Can#10 is bouncing around 130
Can#3 is around 140
Can#2 is fluctuating "50 to 80"
Other machines have higher readings in T2 for example
Can#11 is around 250
Can#10 is around 190
Can#3 is around 260
Can#2 is around 330
Looking at 3 years history data of the flame detector and we found out that T4 readings were not exceeding 180 except can#3 detector was around 220 and they start to drop gradually over time. On other trains looking 3 years back I can see most detectors were reading above 300. yes they have also dropped gradually over time but still considered acceptable an average of 200 to 250. What I am trying to say here that it is not really a new problem that just appeared, except can#11 which is showing 50.
Checks that we already did:
- Alignment of the flame detectors pipe and flanges with the holes in the liners. As per our mechanical group it was found ok?
- Wiring checks are done and found ok
- We confirmed that the right Honeywell scanner part number for LHE system is being used (GE oil & gas part# RRO58985, Manufacturer P/N LG1093AA36, GE P/N 261A1812P014)
- We swapped T4 detectors with T1 detectors and we noticed that those scanners which were reading low in T4 are showing a good reading when installed in T1 and vice versa
- Wheel space after inner thermocouples have a difference of 200 deg F, A = 660 while B = 460, most probably this is a TC failure and it is there since few months unless you have any other advice.
- No dust found on the flame detectors lenses; actually we still have a low reading even after replacement?
- IGV is going wide open @ noon time and it around 56 in night time this is happening in all trains with the change of ambient temperature, however in T4 two months ago this was not happening and can#11 detector was a little higher (100)
- Exhaust readings from TC#1 to TC#13 are (1025, 1021, 992, 1003, 1003, 1001, 1024, 1010, 1003,1001, 1002, 1010)
- Exhaust TC allowable speared TTXSPL (249 F)
- Exhaust TC actual speared TTXSP1 (29 F)
- TNH 4720 rpm sometimes @ noon time increases to 4870
- TNL 4280 to 4314 rpm
- CPD (88 to 95 psi) night to day
- Compressor inlet temp (85 to 112 F) night to day
- Compressor discharge temp (130 to 149 F) night to day
- Ambient air pressure 13.6 PSIA other units are 14.3 PSIA, any effect?
- Exhaust duct pressure 0.2 psi other units are 0.04, any effect?
- P2 pressure 239 psi
- Differential pressure across intake filters 4.2” h2o other unit around 3” h2o
- SRV 29%
- GCV 43%
- IGV (56 to 78 DEG) night to day and in some days it goes wide open when TNH exceed 94%
- Fuel gas temp (130 to 149 F) night to day same as others
- Turbine compartment temp reaches (150 F) which is almost (15 F) higher than other trains
Concerns that I want know:
- Is there any way to confirm fuel to air ratio here to ensure proper combustion? If yes, how? As of my knowledge fuel ratio is maintained by controlling P2 at set point which is calculated by the formula "FPRG = (TNH * FPKGNG) + FPKGNO" which is "FPRG= (TNH * 2.9) - 29" in our case, but what about air ratio? Is IGV adjusting to maximize exhaust temperature only or it will adjust itself in a trail to optimize the combustion and maintain a certain air to fuel ratio?
- I just figure out that FDG the fuel gas flow transmitter is faulty and showing 0, does it have any effect?
- Is there any recommendation to replace that Honeywell scanner with a conventional 4-20 ma one? Do you think this would improve the readings?
- Is there any specific clearance between the tip of the scanner pipe and the liner wall?
- In the inner part of the scanner pipe we have a small hole, what is the purpose of that hole, is it there to prevent condensation on the lens?
- Could there be an issue with the fuel nozzle itself especially the one in can#11? Is it possible to adjust it to control fuel quantity and direction in to the linear? Do you think it is wise to try swapping fuel nozzles?
Please advice? I am ready to provide any additional data required to analyze this problem. FYI, I have already read this article http://www.control.com/thread/1226432295#1226779774.
Thanks in advance and looking for your valuable feedback
This is my first post in this wonderful website, as I was only a reader since a long time ago.
In my plant we have 4 GE 5002D Gas Turbine which is a 2 shaft mechanical drive machine in a combined cycle application. originally the combustion system was a DLN system but 3 years back we did a retrofit to LHE combustion system. We experienced different flame counts on different machines.
2 months ago we had a flame out trip on machine (T4). we were suspecting the flame detectors to be the problem and we did replace 3 out 4 scanners and restart the machine. the situation improved since most of the readings went above 100 while they were around 55 to 80. Then, 2 weeks after the forth scanners reading dropped down to 50. We are investigating why we have low flame detectors reading on the fourth machine (T4)? That is reading lower counts than other machines, here are the current readings:
Can#11 is currently very low 50
Can#10 is bouncing around 130
Can#3 is around 140
Can#2 is fluctuating "50 to 80"
Other machines have higher readings in T2 for example
Can#11 is around 250
Can#10 is around 190
Can#3 is around 260
Can#2 is around 330
Looking at 3 years history data of the flame detector and we found out that T4 readings were not exceeding 180 except can#3 detector was around 220 and they start to drop gradually over time. On other trains looking 3 years back I can see most detectors were reading above 300. yes they have also dropped gradually over time but still considered acceptable an average of 200 to 250. What I am trying to say here that it is not really a new problem that just appeared, except can#11 which is showing 50.
Checks that we already did:
- Alignment of the flame detectors pipe and flanges with the holes in the liners. As per our mechanical group it was found ok?
- Wiring checks are done and found ok
- We confirmed that the right Honeywell scanner part number for LHE system is being used (GE oil & gas part# RRO58985, Manufacturer P/N LG1093AA36, GE P/N 261A1812P014)
- We swapped T4 detectors with T1 detectors and we noticed that those scanners which were reading low in T4 are showing a good reading when installed in T1 and vice versa
- Wheel space after inner thermocouples have a difference of 200 deg F, A = 660 while B = 460, most probably this is a TC failure and it is there since few months unless you have any other advice.
- No dust found on the flame detectors lenses; actually we still have a low reading even after replacement?
- IGV is going wide open @ noon time and it around 56 in night time this is happening in all trains with the change of ambient temperature, however in T4 two months ago this was not happening and can#11 detector was a little higher (100)
- Exhaust readings from TC#1 to TC#13 are (1025, 1021, 992, 1003, 1003, 1001, 1024, 1010, 1003,1001, 1002, 1010)
- Exhaust TC allowable speared TTXSPL (249 F)
- Exhaust TC actual speared TTXSP1 (29 F)
- TNH 4720 rpm sometimes @ noon time increases to 4870
- TNL 4280 to 4314 rpm
- CPD (88 to 95 psi) night to day
- Compressor inlet temp (85 to 112 F) night to day
- Compressor discharge temp (130 to 149 F) night to day
- Ambient air pressure 13.6 PSIA other units are 14.3 PSIA, any effect?
- Exhaust duct pressure 0.2 psi other units are 0.04, any effect?
- P2 pressure 239 psi
- Differential pressure across intake filters 4.2” h2o other unit around 3” h2o
- SRV 29%
- GCV 43%
- IGV (56 to 78 DEG) night to day and in some days it goes wide open when TNH exceed 94%
- Fuel gas temp (130 to 149 F) night to day same as others
- Turbine compartment temp reaches (150 F) which is almost (15 F) higher than other trains
Concerns that I want know:
- Is there any way to confirm fuel to air ratio here to ensure proper combustion? If yes, how? As of my knowledge fuel ratio is maintained by controlling P2 at set point which is calculated by the formula "FPRG = (TNH * FPKGNG) + FPKGNO" which is "FPRG= (TNH * 2.9) - 29" in our case, but what about air ratio? Is IGV adjusting to maximize exhaust temperature only or it will adjust itself in a trail to optimize the combustion and maintain a certain air to fuel ratio?
- I just figure out that FDG the fuel gas flow transmitter is faulty and showing 0, does it have any effect?
- Is there any recommendation to replace that Honeywell scanner with a conventional 4-20 ma one? Do you think this would improve the readings?
- Is there any specific clearance between the tip of the scanner pipe and the liner wall?
- In the inner part of the scanner pipe we have a small hole, what is the purpose of that hole, is it there to prevent condensation on the lens?
- Could there be an issue with the fuel nozzle itself especially the one in can#11? Is it possible to adjust it to control fuel quantity and direction in to the linear? Do you think it is wise to try swapping fuel nozzles?
Please advice? I am ready to provide any additional data required to analyze this problem. FYI, I have already read this article http://www.control.com/thread/1226432295#1226779774.
Thanks in advance and looking for your valuable feedback