There's a load of 55KW motor, which has ZENER soft starter attach to it. The facility has utility and generator power backup. The soft starter works fine on utility, but when it was powered by generator. It was told to me, the power side of the soft starter burnt up. Later on, it was repaired and works fine again on utility again. Generator is a new installation over there. They are afraid of running this again on the generator. I took some observations. The generator is 225KVA gas powered MAN(German brand). I observed the frequency fluctuates at constant load. It varies like 51.2HZ,53.0Hz, 52.3Hz, 51.2Hz. I also notice that much of the electronics of the generator were bypassed. I also took power factor measurement through a NOKIAN power factor panel. On utility I got 0.99PF, when generator was at no load 0.4PF, when on load 0.01-0.02PF. This power factor is very low. I don't know whether AVR of the generator is working or not.
Technician working their also told me about one thing more. They had two 30KW dryer on star/delta on another machine. One dryer start on star, at certain temperature it shift into delta[I didn't know why the tehnician said after attaining a temperature, I have seen shifting from star/delta on time basis, I confirmed again from him, did the motor convert into delta after attaining a specific time or temperature, he said temperature]. After 5 sec, another dryer of 30KW starts on start[when first motor keeps running on delta, the moment the another motor starts on star, the panel get's shutdown. The siemens PLC S7300 restarts, HMI restarts, motors shutdown. It indicates that maybe due to starting torque it might have causes the voltage to drop.This machine works fine on utility, every equipment of the facility works fine. So this is a clear indication, that there's something wrong with the generator. The generator cannot be change now. I need to do something to make their motors running.To install inverter on every drive that causes the problem, I don't know what to do. I don't have experience on Power Generator, it was told to me that you cannot take PF from the generator, unless the generator is at 40% of it's load. At no load, there's no flow of current, so you cannot take PF measurement. However, I have seen smaller pumps of the generator are running. Like Oil pump, water circulation pump of the generator. I don't want to turn the water pump, oil pump OFF! to take the reading, it's very risky and might cause the generator to suddenly seize and melts it's piston.I was also advised from somebody that maybe the generator one spark plug out of 12 is not working and maybe you are getting fluctuation because of 1 plug not working. Facility technician told me, this generator has been over hauled.This indicates that their are fewer chances of spark plugs to be faulty.Inverter and Soft starters are very expensive that can be installed, I'm afraid of giving them a go ahead,their would be no warranty if they get burnt up due to poor power supply from the generator. I would be solely responsible for any loss that happens. I have seen smaller inverters running on this generator below 10KW.Maybe smaller inverters can run, but not bigger inverters on poor PF. ABB inverters recommend around 0.98PF. I sent mail to ZENER australian soft starter company, but got no response of any kind. Some one said, maybe softstarter got burnt because the firing angle got out, because of changing frequency of the thyristor and because of this it got burnt. Smaller inverter is working, because I think there's no problem of misfiring of thyristor, because of AC->DC then DC->AC, inverter has complete control on frequency and no chance of misfiring because it's using DC as a source. As far as poor PF is concerned. I think maybe poor PF has enough current to give to the motors to get started and although they are very small, and inverters are very small size too. So there might not be heavy current demand. Please suggest what to do.
Technician working their also told me about one thing more. They had two 30KW dryer on star/delta on another machine. One dryer start on star, at certain temperature it shift into delta[I didn't know why the tehnician said after attaining a temperature, I have seen shifting from star/delta on time basis, I confirmed again from him, did the motor convert into delta after attaining a specific time or temperature, he said temperature]. After 5 sec, another dryer of 30KW starts on start[when first motor keeps running on delta, the moment the another motor starts on star, the panel get's shutdown. The siemens PLC S7300 restarts, HMI restarts, motors shutdown. It indicates that maybe due to starting torque it might have causes the voltage to drop.This machine works fine on utility, every equipment of the facility works fine. So this is a clear indication, that there's something wrong with the generator. The generator cannot be change now. I need to do something to make their motors running.To install inverter on every drive that causes the problem, I don't know what to do. I don't have experience on Power Generator, it was told to me that you cannot take PF from the generator, unless the generator is at 40% of it's load. At no load, there's no flow of current, so you cannot take PF measurement. However, I have seen smaller pumps of the generator are running. Like Oil pump, water circulation pump of the generator. I don't want to turn the water pump, oil pump OFF! to take the reading, it's very risky and might cause the generator to suddenly seize and melts it's piston.I was also advised from somebody that maybe the generator one spark plug out of 12 is not working and maybe you are getting fluctuation because of 1 plug not working. Facility technician told me, this generator has been over hauled.This indicates that their are fewer chances of spark plugs to be faulty.Inverter and Soft starters are very expensive that can be installed, I'm afraid of giving them a go ahead,their would be no warranty if they get burnt up due to poor power supply from the generator. I would be solely responsible for any loss that happens. I have seen smaller inverters running on this generator below 10KW.Maybe smaller inverters can run, but not bigger inverters on poor PF. ABB inverters recommend around 0.98PF. I sent mail to ZENER australian soft starter company, but got no response of any kind. Some one said, maybe softstarter got burnt because the firing angle got out, because of changing frequency of the thyristor and because of this it got burnt. Smaller inverter is working, because I think there's no problem of misfiring of thyristor, because of AC->DC then DC->AC, inverter has complete control on frequency and no chance of misfiring because it's using DC as a source. As far as poor PF is concerned. I think maybe poor PF has enough current to give to the motors to get started and although they are very small, and inverters are very small size too. So there might not be heavy current demand. Please suggest what to do.