Hi All,
Firstly, i would like to thank all members and moderators for this wonderful and amazing site over here. it provides so much help and information.
Problem:
we have a combined cycle module composed of 2XGE Frame 9FA+E GTs + 1 Alstom ST (Overall power is about 750 MW). few days ago we had a very abnormal behavior of both GTs.
what happened is that both GTs were running at base load about 220 MW each at rated 50 HZ and suddenly the grid frequency dropped down to 48.8 HZ (2932 rpm) and here is the recorded responses:
1. GTs MW increased to 309 MW in one unit and 310 MW in the other for 10 seconds.
2. ST MW increased about 20 MW from base load (Steam control valves were 100% open (Sliding pressure control)).
3. Exhaust temperature increased about 4 F in both GTs.
4. Exhaust mass flow decreased about 30 lbm/sec in both units.
5. during the 10 seconds MW transient Mk VI had an alarm "Backup exhaust temperature reference selected" this alarm was toggling true and false.
6. after 10 sec, MW decreased automatically till back to normal base load values.
7. No recorded alarms from G60 relays to MK VI (to be clear, no one ever tried to log in the relay and check the internal event list yet)
8. control team at site did not backup the Mk VI trip_log live files during the incident and hence we do not have any MK VI trends only we are depending on Historian trends.
9. currently i am away from site, but they confirmed that as historian trend do show the transient increase in MW but never showing any increase in FSR/SRV/GCVs feedbacks.
Technical information:
GT is GE frame 9FA+E, dual fuel
DLN2.0+
Fuel used during incident was natural gas
Control system is MK VI TMR
Rated speed is 3000 rpm (50 HZ)
GTs are running for 4 Years now
one theory i was thinking about is that, as units were at base load so FSRT was active --> when grid frequency dropped --> CPD decreased --> TTRXP increased --> FSRT increased --> more fuel injected into the turbine --> more MW.
but the drawbacks of this theory is that, Trend is not showing any FSR changes and even if the resolution of the trend was not high enough to record this, increase in MW can not be that high (almost 40 % of rated MW) and if this is true why backup ref control came into action.
second theory, there was some kind of electrical fault in the grid that caused High transient current in Generator terminals and hence transient increase in MW.
but if this is true, why G60 did not announce any kind of faults/alarms or even trip to MK VI. and also, why ST did not had the same increase in MW as the three units are connected to the same grid and should see the same fault.
i will try to upload screen shots for trends.
and in the mean time, i wish if anyone have any theories about what could actually happened to help us understand it.
and am appreciating all replies and comments in advance.
Thanks.
Firstly, i would like to thank all members and moderators for this wonderful and amazing site over here. it provides so much help and information.
Problem:
we have a combined cycle module composed of 2XGE Frame 9FA+E GTs + 1 Alstom ST (Overall power is about 750 MW). few days ago we had a very abnormal behavior of both GTs.
what happened is that both GTs were running at base load about 220 MW each at rated 50 HZ and suddenly the grid frequency dropped down to 48.8 HZ (2932 rpm) and here is the recorded responses:
1. GTs MW increased to 309 MW in one unit and 310 MW in the other for 10 seconds.
2. ST MW increased about 20 MW from base load (Steam control valves were 100% open (Sliding pressure control)).
3. Exhaust temperature increased about 4 F in both GTs.
4. Exhaust mass flow decreased about 30 lbm/sec in both units.
5. during the 10 seconds MW transient Mk VI had an alarm "Backup exhaust temperature reference selected" this alarm was toggling true and false.
6. after 10 sec, MW decreased automatically till back to normal base load values.
7. No recorded alarms from G60 relays to MK VI (to be clear, no one ever tried to log in the relay and check the internal event list yet)
8. control team at site did not backup the Mk VI trip_log live files during the incident and hence we do not have any MK VI trends only we are depending on Historian trends.
9. currently i am away from site, but they confirmed that as historian trend do show the transient increase in MW but never showing any increase in FSR/SRV/GCVs feedbacks.
Technical information:
GT is GE frame 9FA+E, dual fuel
DLN2.0+
Fuel used during incident was natural gas
Control system is MK VI TMR
Rated speed is 3000 rpm (50 HZ)
GTs are running for 4 Years now
one theory i was thinking about is that, as units were at base load so FSRT was active --> when grid frequency dropped --> CPD decreased --> TTRXP increased --> FSRT increased --> more fuel injected into the turbine --> more MW.
but the drawbacks of this theory is that, Trend is not showing any FSR changes and even if the resolution of the trend was not high enough to record this, increase in MW can not be that high (almost 40 % of rated MW) and if this is true why backup ref control came into action.
second theory, there was some kind of electrical fault in the grid that caused High transient current in Generator terminals and hence transient increase in MW.
but if this is true, why G60 did not announce any kind of faults/alarms or even trip to MK VI. and also, why ST did not had the same increase in MW as the three units are connected to the same grid and should see the same fault.
i will try to upload screen shots for trends.
and in the mean time, i wish if anyone have any theories about what could actually happened to help us understand it.
and am appreciating all replies and comments in advance.
Thanks.