During trip the machine was operating in Premix mode at 125 MW. In this mode only the Gas control valves PM1 and PM4 only will be in service and D5 valve will be in purge mode.
Finally the fault investigation revealed that the GT 9fa trip was a result of fluctuation in the gas control valve (GCV1). The servo for the GCV1 was replaced with the new one and the machine was started and running normal.
There are two things made me to confuse.
1). why the D5 valve got fluctuation when the machine is operating in premix mode. (I know it is almost at the juncture of Mode change over to PPM which brings Diffusion into service) {(around 125 mw and TTRF is about 1250. i don't know the exact value as i am working on field and not on desk)}. we observed no fluctuation in load and TTRF.
2). As already flame established in all the combustion chambers and machine running at 125 MW (I know two out of four flame scanners fail to detect flame leads to trip) how it will leads to machine trip on loss of flame? and during investigation by my shift charge it came to conclusion that becoz of fluctuation in the gas control valve (GCV1) it leads to trip. but how the fluctuation in GCV1-D5 have affect on loss of flame signal.
waiting for your valuable replies....
Finally the fault investigation revealed that the GT 9fa trip was a result of fluctuation in the gas control valve (GCV1). The servo for the GCV1 was replaced with the new one and the machine was started and running normal.
There are two things made me to confuse.
1). why the D5 valve got fluctuation when the machine is operating in premix mode. (I know it is almost at the juncture of Mode change over to PPM which brings Diffusion into service) {(around 125 mw and TTRF is about 1250. i don't know the exact value as i am working on field and not on desk)}. we observed no fluctuation in load and TTRF.
2). As already flame established in all the combustion chambers and machine running at 125 MW (I know two out of four flame scanners fail to detect flame leads to trip) how it will leads to machine trip on loss of flame? and during investigation by my shift charge it came to conclusion that becoz of fluctuation in the gas control valve (GCV1) it leads to trip. but how the fluctuation in GCV1-D5 have affect on loss of flame signal.
waiting for your valuable replies....