Orifices are used for lots of different things, not just to develop a differential pressure in order to be able to measure flow-rate. They are also commonly used to reduce flow-rates to protect equipment. In this system, they are used for both purposes.
The "bleed" valve you speak of, fabio9, is on the manifold block to which the hydraulic accumulator is affixed. Under normal operation, the "bleed" valve (it should really be called a drain valve) should be closed--and that ensures the hydraulic accumulator has a chance of working correctly. The isolation valve on the other side of the hydraulic accumulator (which is often called the "block valve" (block and bleed--get it?)) should be OPEN at all times when the unit is running (and even when it's not) so the hydraulic accumulator has a chance of working correctly. What does the hydraulic accumulator do? Well, if the IGVs have to move suddenly and quickly, the accumulator will provide additional hydraulic oil to the system to prevent a lag in IGV movement/operation. And, it also helps to prevent dips in hydraulic system pressure when high flows do occur. To do that, the hydraulic accumulator has to be properly charged (usually with an inert gas, such as nitrogen), AND the isolation (block) valve has to be fully open, and the drain (bleed) valve has to be fully closed. Otherwise, the accumulator will not function properly. MANY people do not learn how to properly check the accumulator charge and end up losing the charge, and then when they try to add nitrogen they don't actually get any nitrogen into the accumulator bladder. Finally, a LOT of people misidentify the block (isolation) and bleed (drain) valves, and they both either get opened or closed. It would appear to me that GE Belfort has tried to mitigate the possibility that the bleed valve was inadvertently left open by putting a very small orifice in the outlet of the bleed (drain) valve. The purpose of the drain valve is to remove pressurized hydraulic oil from the accumulator (AFTER the isolation (block) valve has been closed). They are sneaky little devils, those French.... ;-)
The hydraulic oil (from line OH (Oil-Hydraulic) see how they did that?) then goes to one side of VH3-1--which is a hydraulic dump valve assembly. In order to get high-pressure hydraulic oil from the electro-hydraulic servo valve (90TV-1)), through the hydraulic dump valve, and into the double-acting piston of the IGV actuator, HM3-1, the hydraulic dump valve has to be in the proper position. Trip Oil (from the line OLT (Oil-Lube, Trip)--see how that works??!?!!) pressure moves the hydraulic dump valve spool piece to allow high-pressure hydraulic oil to get from the electro-hydraulic servo valve to the IGV actuator piston to make it move. OIL IS ONLY FLOWING TO/FROM THE IGV ACTUATOR WHEN THE IGVs NEED TO MOVE--otherwise, it is a static system (no oil movement to or from). (The electrohydraulic servo-valve controls that--on order from the Mark*.)
There appear to be two 0.156" diameter orifices, one in each line to/from each side of the IGV actuator double-acting piston. GE Belfort must believe this is necessary to dampen any excessive IGV movement due to excessive high-pressure hydraulic oil flow-rates. (Never personally seen this before, but, as we know, those French are NEVER satisfied to leave decades-old engineering practices and principles alone. They are, after all, French--so, their way is (and MUST BE) better. And because they can change things, they will. No other reason required--if possible, it will be unnecessarily and needlessly complicated without explanation. Because they can.)
The last thing of note in the P&ID is the IGV solenoid valve, 20TV-1. In order to get OLT (Trip Oil) to the hydraulic dump valve, VH3-1, 20TV-1 has to be energized ("excited" as ControlsGuy25 said--gotta love that word: excited).
The one thing I'm not sure about on that P&ID is the device with the LITTLE, TINY 0.03" diameter orifice which is just after the 40 micron hydraulic supply filter, FH5-1, on the left of the drawing and just before the bleed (drain) valve. I believe that might be a check valve with a very small orifice drilled in it to allow flow in the reverse direction. In TRUE GE Belfort fashion, it is NOT identified on the drawing with a device number.... But sometimes these check valves with orifices drilled in them (they are often gravity-operated, swinging check valves) are used to help relieve pressure quickly in the event of an emergency trip, but allow full flow, otherwise. Again, GE Belfort is consistently inconsistent in not properly identifying the device, and the drawing of the device is also suspect and unusual. But--it's French, so it MUST be better, right. Even if it isn't (or can't be!) described.
Gotta run. Hope the shish tawuk is good in Tabuk!!! Man I miss the shish tawuk in Umm Al Quwain in the UAE....! (And the hummus, and the fatayer, and the onions, and the tabouleh, and just about everything else on the menu there! Simply AMAZING!!!)
The "bleed" valve you speak of, fabio9, is on the manifold block to which the hydraulic accumulator is affixed. Under normal operation, the "bleed" valve (it should really be called a drain valve) should be closed--and that ensures the hydraulic accumulator has a chance of working correctly. The isolation valve on the other side of the hydraulic accumulator (which is often called the "block valve" (block and bleed--get it?)) should be OPEN at all times when the unit is running (and even when it's not) so the hydraulic accumulator has a chance of working correctly. What does the hydraulic accumulator do? Well, if the IGVs have to move suddenly and quickly, the accumulator will provide additional hydraulic oil to the system to prevent a lag in IGV movement/operation. And, it also helps to prevent dips in hydraulic system pressure when high flows do occur. To do that, the hydraulic accumulator has to be properly charged (usually with an inert gas, such as nitrogen), AND the isolation (block) valve has to be fully open, and the drain (bleed) valve has to be fully closed. Otherwise, the accumulator will not function properly. MANY people do not learn how to properly check the accumulator charge and end up losing the charge, and then when they try to add nitrogen they don't actually get any nitrogen into the accumulator bladder. Finally, a LOT of people misidentify the block (isolation) and bleed (drain) valves, and they both either get opened or closed. It would appear to me that GE Belfort has tried to mitigate the possibility that the bleed valve was inadvertently left open by putting a very small orifice in the outlet of the bleed (drain) valve. The purpose of the drain valve is to remove pressurized hydraulic oil from the accumulator (AFTER the isolation (block) valve has been closed). They are sneaky little devils, those French.... ;-)
The hydraulic oil (from line OH (Oil-Hydraulic) see how they did that?) then goes to one side of VH3-1--which is a hydraulic dump valve assembly. In order to get high-pressure hydraulic oil from the electro-hydraulic servo valve (90TV-1)), through the hydraulic dump valve, and into the double-acting piston of the IGV actuator, HM3-1, the hydraulic dump valve has to be in the proper position. Trip Oil (from the line OLT (Oil-Lube, Trip)--see how that works??!?!!) pressure moves the hydraulic dump valve spool piece to allow high-pressure hydraulic oil to get from the electro-hydraulic servo valve to the IGV actuator piston to make it move. OIL IS ONLY FLOWING TO/FROM THE IGV ACTUATOR WHEN THE IGVs NEED TO MOVE--otherwise, it is a static system (no oil movement to or from). (The electrohydraulic servo-valve controls that--on order from the Mark*.)
There appear to be two 0.156" diameter orifices, one in each line to/from each side of the IGV actuator double-acting piston. GE Belfort must believe this is necessary to dampen any excessive IGV movement due to excessive high-pressure hydraulic oil flow-rates. (Never personally seen this before, but, as we know, those French are NEVER satisfied to leave decades-old engineering practices and principles alone. They are, after all, French--so, their way is (and MUST BE) better. And because they can change things, they will. No other reason required--if possible, it will be unnecessarily and needlessly complicated without explanation. Because they can.)
The last thing of note in the P&ID is the IGV solenoid valve, 20TV-1. In order to get OLT (Trip Oil) to the hydraulic dump valve, VH3-1, 20TV-1 has to be energized ("excited" as ControlsGuy25 said--gotta love that word: excited).
The one thing I'm not sure about on that P&ID is the device with the LITTLE, TINY 0.03" diameter orifice which is just after the 40 micron hydraulic supply filter, FH5-1, on the left of the drawing and just before the bleed (drain) valve. I believe that might be a check valve with a very small orifice drilled in it to allow flow in the reverse direction. In TRUE GE Belfort fashion, it is NOT identified on the drawing with a device number.... But sometimes these check valves with orifices drilled in them (they are often gravity-operated, swinging check valves) are used to help relieve pressure quickly in the event of an emergency trip, but allow full flow, otherwise. Again, GE Belfort is consistently inconsistent in not properly identifying the device, and the drawing of the device is also suspect and unusual. But--it's French, so it MUST be better, right. Even if it isn't (or can't be!) described.
Gotta run. Hope the shish tawuk is good in Tabuk!!! Man I miss the shish tawuk in Umm Al Quwain in the UAE....! (And the hummus, and the fatayer, and the onions, and the tabouleh, and just about everything else on the menu there! Simply AMAZING!!!)