B
The GT HMI screen displayed indications become similar to the condition when Mark VI panel is Power off (i.e #### marks & black colour tabs). It may however be noted that the HMI indication got restored within around 2-3 minutes of the Trip.
The Mark VI panel was inspected within 3-4 minutes of the trip during which the LEDs of all the modules were found synchronised & healthy (I/Os and Processors).
Following are some of our observations:
1) The TripLog file of trip date did not capture any data. The event list in the triplog file are random and it gives all the possible event which is related to the trip.
2) In the TripLogLive file, it was observed that no data was logged between 11:23:24 & 11:25:37 while the trip occured at 11:23:27 hrs.
3)After GT tripping, no command was generated for generator trip
4) No abnormality seen on MK6 panel/processor (to elaborate no processor, power supply, I/O card failed)
5) Trip log at that time of trip didn't capture any data. (Trip log live was logging data before this trip and after GT startup), it seems data was not captured specifically during this trip.
What can be the possible reason for this???
Please give ur views...
The Mark VI panel was inspected within 3-4 minutes of the trip during which the LEDs of all the modules were found synchronised & healthy (I/Os and Processors).
Following are some of our observations:
1) The TripLog file of trip date did not capture any data. The event list in the triplog file are random and it gives all the possible event which is related to the trip.
2) In the TripLogLive file, it was observed that no data was logged between 11:23:24 & 11:25:37 while the trip occured at 11:23:27 hrs.
3)After GT tripping, no command was generated for generator trip
4) No abnormality seen on MK6 panel/processor (to elaborate no processor, power supply, I/O card failed)
5) Trip log at that time of trip didn't capture any data. (Trip log live was logging data before this trip and after GT startup), it seems data was not captured specifically during this trip.
What can be the possible reason for this???