Problem is that whatever comes from any device (obcjet_identifier) is treated by HD67726 as one device and simply multiplies it to different Position with the right order – roomtem will be all the same in any roomtemXX position, same for Malfunction Code, On/Off.
It looks like En Dest, D Net, D Len, D Add are not addressing device correctly and only pulling information from IP Address in column 2.
Attached BDT scan of BACnet
Config file from SW67726 ADFweb Gateway
wireshark log+EDE from YABE
- IP ADDRESS of SNMP is 10.128.159.11
- IP ADDRESS of BACnet is 10.128.159.16 for gateway and 10.128.159.13 for BACnet device
- Instance of BCAnet gateway is 10 and BACnet device is 19
- In BACnet subnet there are 34 instance with number 0190002 to 0190036 their MAC address number are 50:230:2:0:0:0 to 83:230:2:0:0:0 according to the BDT_discovery.PNG file attached.
- In wireshark trace rout as for example Object_Identifier 190002 is in HEX 32:E6:2:0:0:0 (SADR: 32:e6:02:00:00:00 (32:e6:02:00:00:00)) – see bacnet_comm.pcapng file.
- If nothing happen on network ONLY 1 Object_Identifier is responding to Who Is – I Am call – but it’s pretty random one. If I reset BACnet divce (GW-BAC) it will change from one to another.
- If I try to pull some data from any Obcjet_Identifier by YABE or BDT trace rout seems to be correct.
- In SW67726 section BACnet Read columns IP Address, Object Type, Instance, Property, NByte was inserted by function Import EDE (example attached 5_EDE.csv)