We are operating GE7FA DLN 2.6 Gas turbines,
The scenario is like this, M/C was operating on Base load, suddenly there was a alarm of "PM3 GCV out of position alarm & M/C got tripped.
In the field it was found that there was heavy oil leak from the Fuel gas compartment,, Operator didn't have any idea from where the oil was leaking, because it was spreading all over like shower. Later on it was found that PM3 GCV hydraulic oil supply line completed got detached from its location (stainless steel ferulle got sheared off).
We Switched off the hydraulic & lube oil pump after GT reached to zero speed (we must not stop the lube oil system when m/c at speed).
We checked the trend, Hydraulic oil pressure immediately dropped from 115 bar to 35 bar when M/c got trip.
My argument is whether it is advisable in such a situation to stop hydraulic even though m/c is on rotation?
because of the heavy shaft lift oil supply needed to lift the shaft to form hydro dynamic film ( in GE 7FA machine the same hydraulic supply goes to lifting shaft through solenoid v/v 20QB & pump compensator)
We resumed the lube oil supply to the bearings after 1.5 hours of M/c trip. Is it advisable to stop the lube oil supply when M/C tripped from base load? because bearings are very hot it requires some medium of cooling to save the babit metal of the bearing.
If we stop the hydraulic supply we would have save the oil spillage, for your information we topped up 31 drums of oil to restore the lube oil tank to normal level.
please give us the advise what to do in such a situation to control the lube oil spillage
Regards,
Parag
The scenario is like this, M/C was operating on Base load, suddenly there was a alarm of "PM3 GCV out of position alarm & M/C got tripped.
In the field it was found that there was heavy oil leak from the Fuel gas compartment,, Operator didn't have any idea from where the oil was leaking, because it was spreading all over like shower. Later on it was found that PM3 GCV hydraulic oil supply line completed got detached from its location (stainless steel ferulle got sheared off).
We Switched off the hydraulic & lube oil pump after GT reached to zero speed (we must not stop the lube oil system when m/c at speed).
We checked the trend, Hydraulic oil pressure immediately dropped from 115 bar to 35 bar when M/c got trip.
My argument is whether it is advisable in such a situation to stop hydraulic even though m/c is on rotation?
because of the heavy shaft lift oil supply needed to lift the shaft to form hydro dynamic film ( in GE 7FA machine the same hydraulic supply goes to lifting shaft through solenoid v/v 20QB & pump compensator)
We resumed the lube oil supply to the bearings after 1.5 hours of M/c trip. Is it advisable to stop the lube oil supply when M/C tripped from base load? because bearings are very hot it requires some medium of cooling to save the babit metal of the bearing.
If we stop the hydraulic supply we would have save the oil spillage, for your information we topped up 31 drums of oil to restore the lube oil tank to normal level.
please give us the advise what to do in such a situation to control the lube oil spillage
Regards,
Parag