We have two GE frame-6 GT at our plant complex which operate in parallel with GRID. Both the GT operate in droop mode. The running load on GTG-A and GTG-B is maintained near to 22MW each. The load on GRID remains around 4MW. GTG-B is kept on ISO-Standby mode i.e in case of GRID tripping, this machine will switch to ISO mode. Recently one incident happened at our complex. The grid frequency gone to 50.5Hz and GRID got isolated at this point by IPR relay at over frequency protection. Load shedding took place at the complex and a load of around 15MW was shed by Load Shedding System. Load Shedding System keeps monitoring the total generation and connected load and if any of the source get tripped, excess of load is shed. After the transient period and execution of Load Shedding, GTG-A was observed running at 21.5MW, GTG-B (now ISO-machine) was found running at 11.5MW. The IPR relay (MICOM P343) disturbance recorder show a load of around 27MW on GRID feeder just before tripping.
I could figure out that due to droop characteristics of governors of both the GT, they were supposed to throw load due to over-frequency at GRID. If, I take 27MW a reliable value, then we can say that both the GTG should be running at a total generation of (22+22+4-27) = 21MW i.e. during the transition phase, before opening of GRID breaker the generation from each GTG should be around 10.5MW each.
My query is how the GTG-A and GTG-B governors would have acted after tripping of GRID? How much time GTG-A will take to regain the thrown load (start generating) the same power as it was generating before the transient over frequency? From the results, it is looking like that the GT-A governor acted very fast and Load Shedding System recorded its generation near to 21.5MW before starting shedding sequence. Also, what will be the speed reference for GTG-B after it switch over to ISO mode and how fast the action of GTG-B machine will be? What will be the system frequency immediately after de-synchronization from GRID?
How this problem of over frequency can be tackled? Should we go for more conservative over frequency setting for Islanding relay or should we go for increasing the speed droops for governors?
I could figure out that due to droop characteristics of governors of both the GT, they were supposed to throw load due to over-frequency at GRID. If, I take 27MW a reliable value, then we can say that both the GTG should be running at a total generation of (22+22+4-27) = 21MW i.e. during the transition phase, before opening of GRID breaker the generation from each GTG should be around 10.5MW each.
My query is how the GTG-A and GTG-B governors would have acted after tripping of GRID? How much time GTG-A will take to regain the thrown load (start generating) the same power as it was generating before the transient over frequency? From the results, it is looking like that the GT-A governor acted very fast and Load Shedding System recorded its generation near to 21.5MW before starting shedding sequence. Also, what will be the speed reference for GTG-B after it switch over to ISO mode and how fast the action of GTG-B machine will be? What will be the system frequency immediately after de-synchronization from GRID?
How this problem of over frequency can be tackled? Should we go for more conservative over frequency setting for Islanding relay or should we go for increasing the speed droops for governors?