M
We have two gas turbines; control system of one is Mark-II (TG-701) and other is Mark-V (TG-702). Currently Mark-II is on “ISO” while TG-702 is on “DROOP”. We are facing load variation problem. TG-702 picks load of 1.5 MW and TG-701 drops load of 1.5 MW simultaneously. Pressure transmitter is installed on inlet fuel gas of both turbines. Inlet Fuel Pressure of TG-702 shows increases up to 400 NMC and TG-701 shows decreases up to 400 NMC simultaneously. We conformed that no heavy machine / motor start or stop at that time.
We took real time plot of fuel gas from TG-702 (Mark-V), detail of observation is as below.
• FAG (GCV Servo current) shows almost constant reading while FAGR (SRV Servo Current) varies up to 4.0 units approximately.
• GCV_FDBACK and GCV_OUTPUT show almost constant value while minor changes observe in FSGR, GRV_OUTPUT and P2_Pressure.
From above mentioned detail, we come to conclude that SRV of TG-702 might be suspected. Please share your knowledge about that problem. Also suggest what other things we should look in such load variation problem.
We took real time plot of fuel gas from TG-702 (Mark-V), detail of observation is as below.
• FAG (GCV Servo current) shows almost constant reading while FAGR (SRV Servo Current) varies up to 4.0 units approximately.
• GCV_FDBACK and GCV_OUTPUT show almost constant value while minor changes observe in FSGR, GRV_OUTPUT and P2_Pressure.
From above mentioned detail, we come to conclude that SRV of TG-702 might be suspected. Please share your knowledge about that problem. Also suggest what other things we should look in such load variation problem.