Hello all,
I took vibration measurement on HV Motor,
RPM: 990
Synch RPM: 1000
Poles: 6
No. Of Rotor Bars: 88
1XRBPF(Rotor Bar Pass Freq)= 88*990=87120 RPM/60= 1452 Hz
2XRBPF= 2904
2xLF= 100Hz
Bearings: 6324 & 6319
I got very less vibration in overall amplitude. But my concern is when took high frequency spectrum, I get 1XRBPF (Rotor Bar Pass Freq) with 2xLF (Line freq) sidebands and 2XRBPF with those sidebands as well.
2XRBPF amplitude is higher than the 1XRBPF.
There is some sort of rattling noise coming from the motor. There is no bearing damage as per the spectrum because of low vibration and less G values as well.
As per my study I found that 2XRBPF with 2xLF sidebands is much more unusual fault and may indicate the looseness of rotor bars.
Anyone has any idea or came across this type of problem before, please share some ideas or vies.
Thank you
RPM: 990
Synch RPM: 1000
Poles: 6
2XRBPF= 2904
2xLF= 100Hz
Thank you