Diagnostic Alarms at time of discovery:
previously in:
0 R VOTING MISMATCH FPG1
0 R VOTING MISMATCH FPRG
0 R VOTING MISMATCH FSRSR
currently in:
1 S VOTING MISMATCH FSGR
The problem that is being reported by those operating the turbine is as follows:
A sharp downward spike in megawatts, followed from seconds to minutes later by a sharp upward spike. This happens intermittently, sometimes in bundles of 3 spread over a few hours. With a day to several between them.
For pretty much all noted occurrences, the turbine has been in speed control.
The problem, based on chart analysis, appears to be a drop in fuel flow caused by a sudden closing down of the SRV. The GCV position signal shows no initial action, though immediately afterwards FSR reacts to stabilize the situation. Pressures before the SRV rises at the onset of the event as the intervalve pressure drops. The flow usually only drops for a few seconds.
These are the values I found on Datalist 15 GAS RATIO VALVE CONTROL:<pre>
NAME MEDIAN UNITS R S T
FPRG1 252.9 PSI 253.3 252.5 252.9
FPRGOUT -4.22 V DC -4.22 -4.21 -4.22
FPRGBAK -4.20 V DC -4.21 -4.18 -4.20
FSGR_v -3.15 V DC -3.14 -5.75 -3.10
FSGR 23.28 % STR 23.29 60.48 23.28
FAGR 2.51 mA 2.51 -4.40 2.69
FPG1 251.9 PSI 253.7 251.9 251.6
FSRSR 4.10 V DC 4.07 4.13 4.10
FSKGRG V/% 0.0699 0.0715 0.0715
FSKGRO V DC 1.51 1.43 1.4
We have 2 LVDTs associated with this valve: 96SR-1 (4A) and 96SR-2 (4B).
According the the actual jumpers on each HSAA card and our Elementary diagrams, each HSAA card plays the following roles
R - Provides LVDT excitation to 96SR-1 [through AIO.1 terminals ATB EA(5)&(6)]
Receives 96SR-1 (4A) output [through AIO.1 terminals ATB EA(3)&(4)]
s - Provides LVDT excitation to 96SR-2 [through AIO.1 terminals ATB EA(11)&(12)]
Receives 96SR-2 (4B) output [through AIO.1 terminals ATB EA(9)&(10)]
T - Receives 96SR-1 (4A) & 96SR-2 (4B) outputs (HIGH SELECT) [through the terminals noted above]
I added the terminal numbers because I took voltage readings between each pair to get a comparison.
ATB EA (3) & (4) / 0.634 VAC
ATB EA (9) & (10) / 0.707 VAC
ATB EA (5) & (6) / 1.18 VAC
ATB EA (11) & (12) / 1.34 VAC3</pre>
Though I was a little confused to not see 7 Volts for excitation, I figured it was due to the 3000Hz and my meter. As a side, any help on understanding this would be appreciated.
However, the outputs from both LVDTs seemed proportionally similar to their inputs.
This leads me to think that it's the HSAA card on S that needs replacement, and not the field wiring or LVDT.
The problems with 96SR-2 along with the HIGH select on T seems to start to explain the previously cleared VOTING alarms on the R computer, as 4B must have been the active input to T at that time, rendering R as the 'odd man out'. Initially that had me looking to the LVDT or field wiring as the problem, or even excitation to the LVDT, as the one LVDT is common to S and T, given the list of DIAG alarms. But the voltages have me thinking that I need to replace the HSAA card on S. So...
Can I shut down S, replace the HSAA, and start it up without a trip? I'm assuming that FSKGRG and FSKGRO are stored elsewhere in the computer... where?
Ideally this would be best done with a shutdown and a calibration. But during the summer heat, with a lot on the line, is having a spare HSAA card (jumpers pre-set) standing by and waiting and hoping for the best the best idea? What can go wrong?
Am I missing something, or heading down the wrong road in my assessment? Is there more I can look at while running?
previously in:
0 R VOTING MISMATCH FPG1
0 R VOTING MISMATCH FPRG
0 R VOTING MISMATCH FSRSR
currently in:
1 S VOTING MISMATCH FSGR
The problem that is being reported by those operating the turbine is as follows:
A sharp downward spike in megawatts, followed from seconds to minutes later by a sharp upward spike. This happens intermittently, sometimes in bundles of 3 spread over a few hours. With a day to several between them.
For pretty much all noted occurrences, the turbine has been in speed control.
The problem, based on chart analysis, appears to be a drop in fuel flow caused by a sudden closing down of the SRV. The GCV position signal shows no initial action, though immediately afterwards FSR reacts to stabilize the situation. Pressures before the SRV rises at the onset of the event as the intervalve pressure drops. The flow usually only drops for a few seconds.
These are the values I found on Datalist 15 GAS RATIO VALVE CONTROL:<pre>
NAME MEDIAN UNITS R S T
FPRG1 252.9 PSI 253.3 252.5 252.9
FPRGOUT -4.22 V DC -4.22 -4.21 -4.22
FPRGBAK -4.20 V DC -4.21 -4.18 -4.20
FSGR_v -3.15 V DC -3.14 -5.75 -3.10
FSGR 23.28 % STR 23.29 60.48 23.28
FAGR 2.51 mA 2.51 -4.40 2.69
FPG1 251.9 PSI 253.7 251.9 251.6
FSRSR 4.10 V DC 4.07 4.13 4.10
FSKGRG V/% 0.0699 0.0715 0.0715
FSKGRO V DC 1.51 1.43 1.4
We have 2 LVDTs associated with this valve: 96SR-1 (4A) and 96SR-2 (4B).
According the the actual jumpers on each HSAA card and our Elementary diagrams, each HSAA card plays the following roles
R - Provides LVDT excitation to 96SR-1 [through AIO.1 terminals ATB EA(5)&(6)]
Receives 96SR-1 (4A) output [through AIO.1 terminals ATB EA(3)&(4)]
s - Provides LVDT excitation to 96SR-2 [through AIO.1 terminals ATB EA(11)&(12)]
Receives 96SR-2 (4B) output [through AIO.1 terminals ATB EA(9)&(10)]
T - Receives 96SR-1 (4A) & 96SR-2 (4B) outputs (HIGH SELECT) [through the terminals noted above]
I added the terminal numbers because I took voltage readings between each pair to get a comparison.
ATB EA (3) & (4) / 0.634 VAC
ATB EA (9) & (10) / 0.707 VAC
ATB EA (5) & (6) / 1.18 VAC
ATB EA (11) & (12) / 1.34 VAC3</pre>
Though I was a little confused to not see 7 Volts for excitation, I figured it was due to the 3000Hz and my meter. As a side, any help on understanding this would be appreciated.
However, the outputs from both LVDTs seemed proportionally similar to their inputs.
This leads me to think that it's the HSAA card on S that needs replacement, and not the field wiring or LVDT.
The problems with 96SR-2 along with the HIGH select on T seems to start to explain the previously cleared VOTING alarms on the R computer, as 4B must have been the active input to T at that time, rendering R as the 'odd man out'. Initially that had me looking to the LVDT or field wiring as the problem, or even excitation to the LVDT, as the one LVDT is common to S and T, given the list of DIAG alarms. But the voltages have me thinking that I need to replace the HSAA card on S. So...
Can I shut down S, replace the HSAA, and start it up without a trip? I'm assuming that FSKGRG and FSKGRO are stored elsewhere in the computer... where?
Ideally this would be best done with a shutdown and a calibration. But during the summer heat, with a lot on the line, is having a spare HSAA card (jumpers pre-set) standing by and waiting and hoping for the best the best idea? What can go wrong?
Am I missing something, or heading down the wrong road in my assessment? Is there more I can look at while running?