We have a GE Frame 9E Gas Turbine on our plant. The control system is Mark VI. The generator is Air cooled. Our lube oil system contains the following main pumps
Shaft Driven Main Lube Oil Pump
Auxiliary (AC) Oil Pump
DC Lube Oil Pump [Emergency Lube Oil Pump 88QE]
The system has been working fine for some time but we have been facing the problem that when the DC Lube Oil Pump cuts in due to Lube Oil Header Pressure Low [L63QALX] it does not stop on Auto. There is no manual push button to put the pump on manual and stop it. The DC Lube Oil Pump keeps running and it has to be stopped by forcing the signal [L63QALPUL --> Lube Oil Header Pressure Not Low Pulse to Stop 88QE].
I might add that the Lube Oil Header pressure normalizes as soon as the AC Lube Oil Pump starts (AC supply is restored) and the Lube Oil Header Pressure Transmitter and Pressure Switch [L63QA2L] are also working fine. The two pressure switches installed on the Generator Side of the Lube Oil are also normal and have shown no abnormality.
We suspect that the pulse that is supposed to stop the DC Lube Oil pump is rendered ineffective by the signal [L4QELATCH] that goes high as soon as the DC Lube Oil Pump starts and resets after 30 minutes.
Can anybody please help me in understanding the sequence of DC Lube Oil Pump for GE Frame9E Mark VI system.
The DC Lube Oil Pump is working normally in nearly every other respect, it starts during the Startup sequence as it should for 30 seconds and then stops as it should, it starts when its control knob is moved to the Test Position and stops when the knob is returned to 'Auto' position, it starts for its weekly test and stops BUT the problem only comes when it cuts in due to loss of AC Power.
.
.
.
Any ideas, solutions, suggestions would be welcome.
We have a GE Frame 9E Gas Turbine on our plant. The control system is Mark VI. The generator is Air cooled. Our lube oil system contains the following main pumps
Shaft Driven Main Lube Oil Pump
Auxiliary (AC) Oil Pump
DC Lube Oil Pump [Emergency Lube Oil Pump 88QE]
The system has been working fine for some time but we have been facing the problem that when the DC Lube Oil Pump cuts in due to Lube Oil Header Pressure Low [L63QALX] it does not stop on Auto. There is no manual push button to put the pump on manual and stop it. The DC Lube Oil Pump keeps running and it has to be stopped by forcing the signal [L63QALPUL --> Lube Oil Header Pressure Not Low Pulse to Stop 88QE].
I might add that the Lube Oil Header pressure normalizes as soon as the AC Lube Oil Pump starts (AC supply is restored) and the Lube Oil Header Pressure Transmitter and Pressure Switch [L63QA2L] are also working fine. The two pressure switches installed on the Generator Side of the Lube Oil are also normal and have shown no abnormality.
We suspect that the pulse that is supposed to stop the DC Lube Oil pump is rendered ineffective by the signal [L4QELATCH] that goes high as soon as the DC Lube Oil Pump starts and resets after 30 minutes.
Can anybody please help me in understanding the sequence of DC Lube Oil Pump for GE Frame9E Mark VI system.
The DC Lube Oil Pump is working normally in nearly every other respect, it starts during the Startup sequence as it should for 30 seconds and then stops as it should, it starts when its control knob is moved to the Test Position and stops when the knob is returned to 'Auto' position, it starts for its weekly test and stops BUT the problem only comes when it cuts in due to loss of AC Power.
.
.
.
Any ideas, solutions, suggestions would be welcome.