After performing an "online" compressor wash the following events transpire: Multiple diagnostics on either <r> or <s> computer (occurs on only one computer per instance) FSRS1, FSRSR, FSR2, FSROUT, FPRG, FSRACC, FSRSU, FRST, L4X1, L20CB1X, L20FG1X, L83RX, L4GA, L20WN1X, L60 WQDIR and the Master Protective Lockout.
Gas Valve Control Screen:
Funct name med units <r> <s> <t>
REFER FSR2 75.0 %fsr 75.0 0.0 75.0
REF OUT FSROUT 7.38 V DC 7.38 0.00 7.60
REF BACK FRSBAK 7.38 V DC 7.38 0.00 7.56
POS VOLTS FSG_V -7.34 V DC -7.19 -7.40 -7.34
POSITION FSG 74.53 %STR 74.53 73.86 74.55
CURRENT FAG 0.45 MA 0.54 -8.69 0.45
It appears to me that the <s> computer is trying to force the valve closed, thus the negative current value on FAG. Since this occurs following the online compressor wash could it be that the GCV is hanging up internally? Resetting the computer in question will correct the issue but hardly seems to be an viable solution.
Replaced the GCV LVDT and Servo yesterday (calibrated)and the unit ran at baseload throughout the night w/o any issues. It started approximately 3 minutes following the wash.
Thanks, Mark
Gas Valve Control Screen:
Funct name med units <r> <s> <t>
REFER FSR2 75.0 %fsr 75.0 0.0 75.0
REF OUT FSROUT 7.38 V DC 7.38 0.00 7.60
REF BACK FRSBAK 7.38 V DC 7.38 0.00 7.56
POS VOLTS FSG_V -7.34 V DC -7.19 -7.40 -7.34
POSITION FSG 74.53 %STR 74.53 73.86 74.55
CURRENT FAG 0.45 MA 0.54 -8.69 0.45
It appears to me that the <s> computer is trying to force the valve closed, thus the negative current value on FAG. Since this occurs following the online compressor wash could it be that the GCV is hanging up internally? Resetting the computer in question will correct the issue but hardly seems to be an viable solution.
Replaced the GCV LVDT and Servo yesterday (calibrated)and the unit ran at baseload throughout the night w/o any issues. It started approximately 3 minutes following the wash.
Thanks, Mark