Awaneesh,
If Machine 2's Isochronous Speed Reference is 100.1354 the frequency when running is 50.0677 Hz, +/-0.17 Hz, which is most likely the reason Machine 1 is unloading. The signal names for frequency are SFL1 and SFL2. Even small differences like this can cause the problem being troubleshot here.
I've never seen a Load Gear with an exact rating of 5100/3000. The typical design speed of most GE-design heavy duty gas turbine axial compressors is 5100 RPM, but there is an acceptable operating range of as much as approximately 30 RPM so Load Gear ratios don't have to be exactly 5100 RPM and quite often aren't. Typical ratios I have seen are 5094, 5104, 5120, and 5134.
The problem arises when the Speedtronic turbine shaft speed feedback scaling is set to 5100 RPM from the factory and the commissioning person doesn't check the Load Gear nameplate and change the Speedtronic scaling there can be problems with synchronizing and Isochronous speed control.
I'm only mentioning this because it could also be contributing to the problem being troubleshot here.
This especially happens when two turbines are installed and commissioned at different times.
No; I don't think the problem could be caused by powering-down the Speedtronic panel. <b>Based on the information provided to date</b>, it seems the problem is related to the different TNRI values in the two machines. I don't believe the problem is caused by Machine 1, but rather by the incorrect TNRI of Machine 2.
TNRI can be changed when the unit is operating in Isoch mode, and by the operator observing TNRI while clicking on LOWER SPD/LOAD until the value returns to 100.00, or as close as possible.
I would suggest checking the Load Gear nameplates of both machines for their respective ratios and also checking the speed feedback scaling of the turbine shaft speed sensors of the TTUR card configuration to be certain the scaling matches the nameplate value.
Please write back with more information as you work to resolve this problem.
If Machine 2's Isochronous Speed Reference is 100.1354 the frequency when running is 50.0677 Hz, +/-0.17 Hz, which is most likely the reason Machine 1 is unloading. The signal names for frequency are SFL1 and SFL2. Even small differences like this can cause the problem being troubleshot here.
I've never seen a Load Gear with an exact rating of 5100/3000. The typical design speed of most GE-design heavy duty gas turbine axial compressors is 5100 RPM, but there is an acceptable operating range of as much as approximately 30 RPM so Load Gear ratios don't have to be exactly 5100 RPM and quite often aren't. Typical ratios I have seen are 5094, 5104, 5120, and 5134.
The problem arises when the Speedtronic turbine shaft speed feedback scaling is set to 5100 RPM from the factory and the commissioning person doesn't check the Load Gear nameplate and change the Speedtronic scaling there can be problems with synchronizing and Isochronous speed control.
I'm only mentioning this because it could also be contributing to the problem being troubleshot here.
This especially happens when two turbines are installed and commissioned at different times.
No; I don't think the problem could be caused by powering-down the Speedtronic panel. <b>Based on the information provided to date</b>, it seems the problem is related to the different TNRI values in the two machines. I don't believe the problem is caused by Machine 1, but rather by the incorrect TNRI of Machine 2.
TNRI can be changed when the unit is operating in Isoch mode, and by the operator observing TNRI while clicking on LOWER SPD/LOAD until the value returns to 100.00, or as close as possible.
I would suggest checking the Load Gear nameplates of both machines for their respective ratios and also checking the speed feedback scaling of the turbine shaft speed sensors of the TTUR card configuration to be certain the scaling matches the nameplate value.
Please write back with more information as you work to resolve this problem.