Hello,
WE have one of the new gas turbines frame 5 mark VI controller Moog problem during making dry fire (turning off spark plug & increasing ignition time).
When we reach ignition phase after purge 2 min. the stop valve 20fl1x is open and the servo valve contiguous open and close many times during the flow test and no fuel arrived after check valves, the time between servo valve open and close is in seconds (3-5 sec.)
The parameters before starting is:
1- liquid fuel flow reference = -25%
2- liquid fuel by pass valve servo current= 70%
3- liquid fuel flow = 0
The parameters during starting is :
1- liquid fuel flow reference = 4.5%
2- liquid fuel by pass valve servo current = -15
3- liquid fuel flow read very big value more then 900&
4- also magnetic speed pickup of flow divider same reading more than 500 - 1000 %
so when the flow detected very high value bypass valve servo current go to high positive value more than 74% and after 3 to 4 seconds return to the negative value between -12 to -15 %
Is that the problem in servo valve or in high reading of flow divider magnetic speed pickup so the control valve (MooG) try to reduce the value by increase the bypass?
Is it software problem?
Is the servo current is ok?
Thank you all
Ayman
WE have one of the new gas turbines frame 5 mark VI controller Moog problem during making dry fire (turning off spark plug & increasing ignition time).
When we reach ignition phase after purge 2 min. the stop valve 20fl1x is open and the servo valve contiguous open and close many times during the flow test and no fuel arrived after check valves, the time between servo valve open and close is in seconds (3-5 sec.)
The parameters before starting is:
1- liquid fuel flow reference = -25%
2- liquid fuel by pass valve servo current= 70%
3- liquid fuel flow = 0
The parameters during starting is :
1- liquid fuel flow reference = 4.5%
2- liquid fuel by pass valve servo current = -15
3- liquid fuel flow read very big value more then 900&
4- also magnetic speed pickup of flow divider same reading more than 500 - 1000 %
so when the flow detected very high value bypass valve servo current go to high positive value more than 74% and after 3 to 4 seconds return to the negative value between -12 to -15 %
Is that the problem in servo valve or in high reading of flow divider magnetic speed pickup so the control valve (MooG) try to reduce the value by increase the bypass?
Is it software problem?
Is the servo current is ok?
Thank you all
Ayman