A diesel power plant, consist of 3 generator sets, each installed capacity is 3.1 MW,. 8pf,50hz,actual capacity of each generator now is 2.5 MW, due to running hours and maintenance.
11KV feeder come from the substation to the bus bar of the diesel plant, where the diesel generator sets parallel with, in order to improve voltage, since the 220KV come along a distance of nearly 350 Km, and there is voltage drop.
SSome times the power factor of one generator becomes more leading or capacitive and there is no way to readjust it so as to become. 8 lagg or near, we put it's breaker off before it becomes more capacitive and problems occur.
What are the reasons and how to correct.