Dear All..
GE Fr5-Mk5 control protection system Diag.alarm. The following diagnostic alarms appears in the screen since 2 days with turbine running in Gas fuel mode.
1.TCE1 TMR check trouble,ETR1 {Diag Drop#1696}
for R-S-T controller.
2.TCE1 TMR check trouble,ETR2 {Diag.Drop#1697}for R-S-T controller
3.Voting mismatch,"S" 4ETR1 {C 2278}
4.Voting mismatch,"S" 4ETR2 {C 2279}
5.Voting mismatch ,"S"L12_ACC{C2282}
6.TCE1 HP reading,Hardware trouble for "S"{1680}
By going thro these alarms, I understand that one of the voting {input} from "S" processor has failed and turbine continue running with available 2/3 voting from R and T. I think,that these alarms could be due to failure of NHP speed sensor signal going to TCEA "y" in "P" core OR failure of RD in TCTG trip card OR TCEA "Y" card at Loc3 of "P" core. Am I corect? I need to shut down the turbine in order to diagnose the fault. Could you PLs some one suggest/help solve the problem. Thanx
GE Fr5-Mk5 control protection system Diag.alarm. The following diagnostic alarms appears in the screen since 2 days with turbine running in Gas fuel mode.
1.TCE1 TMR check trouble,ETR1 {Diag Drop#1696}
for R-S-T controller.
2.TCE1 TMR check trouble,ETR2 {Diag.Drop#1697}for R-S-T controller
3.Voting mismatch,"S" 4ETR1 {C 2278}
4.Voting mismatch,"S" 4ETR2 {C 2279}
5.Voting mismatch ,"S"L12_ACC{C2282}
6.TCE1 HP reading,Hardware trouble for "S"{1680}
By going thro these alarms, I understand that one of the voting {input} from "S" processor has failed and turbine continue running with available 2/3 voting from R and T. I think,that these alarms could be due to failure of NHP speed sensor signal going to TCEA "y" in "P" core OR failure of RD in TCTG trip card OR TCEA "Y" card at Loc3 of "P" core. Am I corect? I need to shut down the turbine in order to diagnose the fault. Could you PLs some one suggest/help solve the problem. Thanx