hello everyone
I want to talk about a event occur with me.
I am a shift supervisor in gas plant. the last week, I approved a PTW for instrumentation technician to purge inlet (suction) FI for BLC606C compressor driven by MS5002C from GE controlled by MARK 5, because it was indicate 0 although the machine was on service. when he open the purge valve, these events occur DDS Activate, anti-surge valve opened, and the GT entered under CONTROL TEMPERATURE (exhaust temperature reaches 535 c).
I want to ask, is the purge of FI caused these phenomenon? or the increase of temperature?
if the first answer, how to purge this FI with the machine on service?
best regards
I want to talk about a event occur with me.
I am a shift supervisor in gas plant. the last week, I approved a PTW for instrumentation technician to purge inlet (suction) FI for BLC606C compressor driven by MS5002C from GE controlled by MARK 5, because it was indicate 0 although the machine was on service. when he open the purge valve, these events occur DDS Activate, anti-surge valve opened, and the GT entered under CONTROL TEMPERATURE (exhaust temperature reaches 535 c).