Q
Dear Member control.com
I could like to asking you the question about the 2051TG and 2051TA of rosemount pressure transmitter.
Here is the spec of them
2051T In-Line Pressure Transmitter
Model Measurement Type
G Gage
A Absolute
Code Pressure Ranges (Ranges/ Min. Span)
2051TG1/2/3/4/5
-14.7 to 30 psi/0.3 psi (-1,01 to 2,1 bar/20,7 mbar)
-14.7 to 150 psi/1.5 psi (-1,01 to 10,3 bar/103,4 mbar)
-14.7 to 800 psi/8 psi (-1,01 to 55,2 bar/0,55 bar)
-14.7 to 4000 psi/40 psi (-1,01 to 275,8 bar/2,8 bar)
-14.7 to 10000 psi/2000 psi (-1,01 to 689,5 bar/138 bar)
2051TA1/2/3/4/5
0 to 30 psia/0.3 psia (0 to 2,1 bar/20,7 mbar)
0 to 150 psia/1.5 psia (0 to 10,3 bar/103,4 mbar)
0 to 800 psia/8 psia (0 to 55,2 bar/0,55 bar)
0 to 4000 psia/40 psia (0 to 275,8 bar/2,8 bar)
0 to 10000 psia/2000 psia (0 to 689,5 bar/138 bar)
We are normally use 2051TA for vacuum pressure measurement. Our power plant, condenser vacuum pressure is using 2051TA1 (range 0mmHgA to 760mmHgA).
Refering to above spec, the 2051TG1 and 2051TA1 have same range so my question is can I using 2051TG1 instead of 2051TA1 (in case 2051TA1 failure, and I have spare part of 2051TG1 only) for vacuum pressure measurement? What is the merit and demerit?
Thank you very much.
I could like to asking you the question about the 2051TG and 2051TA of rosemount pressure transmitter.
Here is the spec of them
2051T In-Line Pressure Transmitter
Model Measurement Type
G Gage
A Absolute
Code Pressure Ranges (Ranges/ Min. Span)
2051TG1/2/3/4/5
-14.7 to 30 psi/0.3 psi (-1,01 to 2,1 bar/20,7 mbar)
-14.7 to 150 psi/1.5 psi (-1,01 to 10,3 bar/103,4 mbar)
-14.7 to 800 psi/8 psi (-1,01 to 55,2 bar/0,55 bar)
-14.7 to 4000 psi/40 psi (-1,01 to 275,8 bar/2,8 bar)
-14.7 to 10000 psi/2000 psi (-1,01 to 689,5 bar/138 bar)
2051TA1/2/3/4/5
0 to 30 psia/0.3 psia (0 to 2,1 bar/20,7 mbar)
0 to 150 psia/1.5 psia (0 to 10,3 bar/103,4 mbar)
0 to 800 psia/8 psia (0 to 55,2 bar/0,55 bar)
0 to 4000 psia/40 psia (0 to 275,8 bar/2,8 bar)
0 to 10000 psia/2000 psia (0 to 689,5 bar/138 bar)
We are normally use 2051TA for vacuum pressure measurement. Our power plant, condenser vacuum pressure is using 2051TA1 (range 0mmHgA to 760mmHgA).
Refering to above spec, the 2051TG1 and 2051TA1 have same range so my question is can I using 2051TG1 instead of 2051TA1 (in case 2051TA1 failure, and I have spare part of 2051TG1 only) for vacuum pressure measurement? What is the merit and demerit?
Thank you very much.