Before asking any questions I want to explain something about the circumstances of one of our GT. GT (Frame 6B) tripped showing following alarms:
1. Excitation overcurrent -1st step at 18:10:34.229
2. Loss of Flame at 18:10:34.589
It is really confusing that for excitation overcurrent GT should not trip it should go to FSNL.
In trip log of GT it was found that at 18:10:33 FPG2 reduced from 19.27 bar to 15.27 bar and at 18:10:34 FPG2 went to 6.25 bar and mean while SRV opening was going down because of servo current in trip log was going down from -26.5% to +72%.
Then we replaced the existing servo of SRV and calibrated it. After calibration we got the following message:
R STATUS: State=116, (0x74)
S STATUS: State=116, (0x74)
T STATUS: State=116, (0x74)
We tried several times to get "Calibration Finished" message but we failed. I didn't know why the above message came???
Another problem we found during runtime of GT:
..........................<R>.......<S>........<T>
Required Position...17.39....17.39......17.39..%
Actual Position......18.31....18.30......18.32 %
Servo Current.......49.69....-27.23.....-26.55 %
Why the servo current of R core is so different than the other two?
It should be mentioned that we have Frame 6B GT and Mark V control system.
1. Excitation overcurrent -1st step at 18:10:34.229
2. Loss of Flame at 18:10:34.589
It is really confusing that for excitation overcurrent GT should not trip it should go to FSNL.
In trip log of GT it was found that at 18:10:33 FPG2 reduced from 19.27 bar to 15.27 bar and at 18:10:34 FPG2 went to 6.25 bar and mean while SRV opening was going down because of servo current in trip log was going down from -26.5% to +72%.
Then we replaced the existing servo of SRV and calibrated it. After calibration we got the following message:
R STATUS: State=116, (0x74)
S STATUS: State=116, (0x74)
T STATUS: State=116, (0x74)
We tried several times to get "Calibration Finished" message but we failed. I didn't know why the above message came???
Another problem we found during runtime of GT:
..........................<R>.......<S>........<T>
Required Position...17.39....17.39......17.39..%
Actual Position......18.31....18.30......18.32 %
Servo Current.......49.69....-27.23.....-26.55 %
Why the servo current of R core is so different than the other two?
It should be mentioned that we have Frame 6B GT and Mark V control system.