I would like to add some more interesting facts and kindly ask for explanation.
We have 4 Frame 5 non-dln turbines running in the island mode. I have found something odd troubleshooting the moog of one of the machines, that randomly changes its bias causing 3% position error - temporary solution we use(unit online) is to recalculate new Null Bias measuring coils voltage and having coil resistance measured before, then downloading the VSVO. This way it's fine for some time, usually until next start-up. I have to mention, that we have already tried three different Moogs with the same result.
Back to the moog story. The odd thing is that each unit SRV, GCV and IGV servo currents change at the same time from one stable value to another one (usually by the step of 3, 4 %). The same time error doesn't change. I have trended hydraulic pressure 96HQ but there is no sign of the event. Also no sign on P125DC and N125DC. I'm running out of ideas what to trend.
Also polarity has been checked many times so far by confiming that MKVI is able to drive the valve by each servo coil separetely.
Although it happens on all four units, the event doesn't occure at the same time looking from unit to unit (see my trends).
Please check the data collected I uploded below:
http://www.speedyshare.com/476835562.html
Do not be surpirsed looking at these trends. One of our machines (G4) also have out of spec, positive Null Bias, since commisioning by GE (MKVI config value -12, changing moogs didn't help, anyway machine is controlled correctly.)
Any explanation on the moog servo current changes? Why all units affected?
We have 4 Frame 5 non-dln turbines running in the island mode. I have found something odd troubleshooting the moog of one of the machines, that randomly changes its bias causing 3% position error - temporary solution we use(unit online) is to recalculate new Null Bias measuring coils voltage and having coil resistance measured before, then downloading the VSVO. This way it's fine for some time, usually until next start-up. I have to mention, that we have already tried three different Moogs with the same result.
Back to the moog story. The odd thing is that each unit SRV, GCV and IGV servo currents change at the same time from one stable value to another one (usually by the step of 3, 4 %). The same time error doesn't change. I have trended hydraulic pressure 96HQ but there is no sign of the event. Also no sign on P125DC and N125DC. I'm running out of ideas what to trend.
Also polarity has been checked many times so far by confiming that MKVI is able to drive the valve by each servo coil separetely.
Although it happens on all four units, the event doesn't occure at the same time looking from unit to unit (see my trends).
Please check the data collected I uploded below:
http://www.speedyshare.com/476835562.html
Do not be surpirsed looking at these trends. One of our machines (G4) also have out of spec, positive Null Bias, since commisioning by GE (MKVI config value -12, changing moogs didn't help, anyway machine is controlled correctly.)
Any explanation on the moog servo current changes? Why all units affected?