Hi, all
Should 0v of 24VDC power system for PLC be connected to ground? Any help or information will be welcome.
Should 0v of 24VDC power system for PLC be connected to ground? Any help or information will be welcome.
Just had this problem on site because one cabinet hand its GND tied to OV (where the equiptment was supplied from) and the the other cabinet (where I ran the control cable to a different PLC) did. Now because there is no standard I am having a tough time putting it back on the installers for shorting out a very expensive peice of electrical equiptment :-/Generally I connect 0 vdc to ground, particularly if there are comms involved. Have seen comm ports with different power supplies not grounded have problems with floating voltages and even disappear in a puff of smoke.