Hey guys,
I am working (remotely) on a GE Frame 7EA (MS7001EA) DLN1 Machine, and there is a table used for a linear interpolator in the logic. In the Mark VIe you can export the table to a PDF within Toolbox, but not sure about the Mark V. Was hoping I could get some instruction here on how to obtain those curve values.
I cannot directly access the running controller, as I am remote, but I do have all of the "Unit 1" files on my laptop, and so I haven't had any trouble getting curve values until I got to this 3D Table. I also have site maintenance personnel available to gather information from the running controller for me as required.
This table uses CSGV and TNHCOR to cross-tabulate a Compressor Ratio Limit, but I cannot find anything in the site files such as a pdf of the table (Which usually S/U Engineers create for posterity).
I am working (remotely) on a GE Frame 7EA (MS7001EA) DLN1 Machine, and there is a table used for a linear interpolator in the logic. In the Mark VIe you can export the table to a PDF within Toolbox, but not sure about the Mark V. Was hoping I could get some instruction here on how to obtain those curve values.
I cannot directly access the running controller, as I am remote, but I do have all of the "Unit 1" files on my laptop, and so I haven't had any trouble getting curve values until I got to this 3D Table. I also have site maintenance personnel available to gather information from the running controller for me as required.
This table uses CSGV and TNHCOR to cross-tabulate a Compressor Ratio Limit, but I cannot find anything in the site files such as a pdf of the table (Which usually S/U Engineers create for posterity).
Attachments
-
129.4 KB Views: 46