We have a transformer of 4 MVA, its Vector group is Dyn 11 (11000 / 3300 volt) step down, load losses are 40.8 KW. If we use this transformer as step up, are the losses are same or will be increase?
Shoaib, you are correct if: the primary-winding and secondary-winding leakage impedances are equivalent; and 2) you are using an "approximate" version of the transformer model, that is, core-loss components are placed at the supply-source voltage terminals.
An aside to Hussain... are you sure load-loss is 40.8kW? What is core-loss?