Vibration transducer Fault alarm

A

Thread Starter

Aliya

Hi all,
Please tell me that how Mark IV and Mark VIe checks for "Vibration transducer Fault" alarm.

when Health Bit "HLTHn" becomes 0 and 1. How control system ensures it?
 
P

Process Value

> when Health Bit "HLTHn" becomes 0 and 1. How control system ensures it? <

Vibration sensor fault detection.

A small DC current is passed through the sensor at all times (3 ma) is circulated through the sensor at all times to detect a fault in the cable or an open input. Ie if the Dc current value falls below a particular value the health bit goes low.
 
The answer to this question, and others like it, are found in the Mark VI System Guide, GEH-6421, specifically Vol. II. And can also be found in the Toolbox Help file on newer versions of Toolbox.
 
Thanks for your reply.

I still have one doubt, this check (sending 3 mA) is used in both Mark IV and Mark VI, or different methods used?

And the health bit only depends on this feedback?
 
P

Process Value

I do not know about mark iv, but mark v, mark vi and mark vie uses the following technique. please go through the mark v application manual, mark vi system manual vol II (VVIB section) detailed diagrams and explanation are given.
 