I would like to ask for opinion or past experience on two of the new problem I am facing now which I believe could be related to each other. My unit is GE Frame 9e with Mark V TMR. The unit just underwent major overhaul with compressor rotor replacement, stator reblading and VIGV reblading.
(i) First Problem
The problem is the VIGV tends to move to open (from fully close at 32deg) when the unit is on cranking mode or when the AHOP is in operation. The movement is slow wrt time.
The VIGV is steady when operated via AUTOCAL or during unit operation.
The two LVDT and servos are new and were replaced during the overhaul as part of maintenance plan. The LVDTs were calibrated and the angle measured= angle feedback.
From the unit PnID, it can be seen that the VIGV is held at last position by the hydraulic oil pressure from the hdyraulic header and accumulator. I believe that the problem might be with the hydraulic system but no work was done in the hydraulic system during the outage.
(ii) Second problem
The problem is that the unit is falling off cooldown. Whenever the unit is selected to on cooldown mode, the unit successfully breakaway but failed to maintain cooldown and goes to standstill. The unit had all the bearings replaced during the outage. We have cranked the unit for 2 days and started up to FSNL for several hours but the result is the same. Could it be resolved by operating the unit for some time or is there any problem which could cause this as well? There has been a thread previously on this problem but the originator did not reply on what was the finding.
Any advice or past experience on the matter would be greatly appreciated.
Thanks
(i) First Problem
The problem is the VIGV tends to move to open (from fully close at 32deg) when the unit is on cranking mode or when the AHOP is in operation. The movement is slow wrt time.
The VIGV is steady when operated via AUTOCAL or during unit operation.
The two LVDT and servos are new and were replaced during the overhaul as part of maintenance plan. The LVDTs were calibrated and the angle measured= angle feedback.
From the unit PnID, it can be seen that the VIGV is held at last position by the hydraulic oil pressure from the hdyraulic header and accumulator. I believe that the problem might be with the hydraulic system but no work was done in the hydraulic system during the outage.
(ii) Second problem
The problem is that the unit is falling off cooldown. Whenever the unit is selected to on cooldown mode, the unit successfully breakaway but failed to maintain cooldown and goes to standstill. The unit had all the bearings replaced during the outage. We have cranked the unit for 2 days and started up to FSNL for several hours but the result is the same. Could it be resolved by operating the unit for some time or is there any problem which could cause this as well? There has been a thread previously on this problem but the originator did not reply on what was the finding.
Any advice or past experience on the matter would be greatly appreciated.