I would like to share a small problem which has started to bug me recently after the replacement of GCV/SRV in one of my unit (GE F9e with Mark V TMR).
Recently the GCV/SRV (combined vlv) was replaced with a spare refurbished valve after the SRV spring broke. However after the replacement, calibration and operation for 1 day, the core for 96SR1 (LVDT#1) of the SRV broke.
The core was found to break at the top at the before the thread. The core broke again after replacement within 1 day.
Observation during unit shutdown (SRV fully closed) as follows:
(i) Holder for LVDT is tightly secured to the vlv stem.
(ii) LVDT assembly is tightly secured to the base of SRV and LVDT holder
(iii) The holder for LVDT could be moved to the left and right. Since the holder is secured to the valve stem, the SRV stem could also rotate when the holder is moved.
Observation when SRV is opened at various percentage (using AUTOCAL) during unit shutdown:
(i) The holder for LVDT could NOT be moved at all.
Observation when unit is in operation (SRV open):
(i) The holder for LVDT could NOT be moved at all.
(ii) The whole valve assembly vibrates.
Observation of another unit of same type:
(i) The holder does not move either when unit is shutdown, SRV open during shutdown or during unit operation.
(ii) The whole valve assembly does not vibrate.
My assumption so far is that the movement of the LVDT holder and vibration of the valve could cause the LVDT core to break. The fact that 96SR2 which is installed on the same holder does not break, I think is due to the distance from the valve stem is closer as compared to 96SR1 (slight movement causes most displacement at furthest distance).
Currently the unit is operating with 1 LVDT (96SR2) only without any problem as the replacement of the LVDT core without resolving the root cause would cause it to break yet again.
Appreciate if anyone have experience similar problem to advice on the possible root cause.
Recently the GCV/SRV (combined vlv) was replaced with a spare refurbished valve after the SRV spring broke. However after the replacement, calibration and operation for 1 day, the core for 96SR1 (LVDT#1) of the SRV broke.
The core was found to break at the top at the before the thread. The core broke again after replacement within 1 day.
Observation during unit shutdown (SRV fully closed) as follows:
(i) Holder for LVDT is tightly secured to the vlv stem.
(ii) LVDT assembly is tightly secured to the base of SRV and LVDT holder
(iii) The holder for LVDT could be moved to the left and right. Since the holder is secured to the valve stem, the SRV stem could also rotate when the holder is moved.
Observation when SRV is opened at various percentage (using AUTOCAL) during unit shutdown:
(i) The holder for LVDT could NOT be moved at all.
Observation when unit is in operation (SRV open):
(i) The holder for LVDT could NOT be moved at all.
(ii) The whole valve assembly vibrates.
Observation of another unit of same type:
(i) The holder does not move either when unit is shutdown, SRV open during shutdown or during unit operation.
(ii) The whole valve assembly does not vibrate.
My assumption so far is that the movement of the LVDT holder and vibration of the valve could cause the LVDT core to break. The fact that 96SR2 which is installed on the same holder does not break, I think is due to the distance from the valve stem is closer as compared to 96SR1 (slight movement causes most displacement at furthest distance).
Currently the unit is operating with 1 LVDT (96SR2) only without any problem as the replacement of the LVDT core without resolving the root cause would cause it to break yet again.
Appreciate if anyone have experience similar problem to advice on the possible root cause.