AF100 OPC server issues

B

Thread Starter

Ben

having installed an AF100 OPC server on the AF100 network with an AC110. I have found no real issues except that I cannot write to a particular data type, MBS.

Have tried using a variety of different OPC clients and all the data types.

Any help?

Thanks
 
L
Can you tell from any of the OPC clients what the access rights for this item are? It may be a read-only point.

Louis Ross
 
K

Kingsun, Ben J

The point is listed as a read and write point in the manual. I actually found out by accident that if (Digital) if 0 and I write a 0 then it goes to 1, if when 0 and I write a 1 it stays 0. visa versa.

Which is pretty bad considering that all other points work well. The version of software is 3.0 for the AF100 OPC server, I have a feeling that there might be a service pack??

Cheers,
BK
 