You say the unit at your site has an adjustable torque converter (Torque Adjuster). If that is true, then I would say the Torque Adjuster limit switches are *NOT* adjusted properly. I'm making this statement with the following caveat: It is a typical GE-design Frame 9E heavy duty gas turbine with no unusual auxiliaries, fuels, or sequencing.
The Torque Adjustor should be set to "purge" speed position to cause the unit to accelerate to *approximately* 20% speed during starting (the actual speed is irrelevant; it's supposed to be 150-160% of rated starting motor current) for the purge period. Once the purge period is complete, the unit should decelerate to 9.5% speed (actually the speed will dip slightly below 9.5%) and the torque adjuster should be set to "firing" speed, which will slowly accelerate the unit up through 10% speed at which time the fuel stop valve is opened, the fuel is set to firing value, and the spark plugs are energized.
When flame is detected, the fuel is cut back to warm-up value and after a short time delay the Torque Adjuster will be pulsed to "accelerate" position to begin accelerating the turbine-generator shaft. After the warm-up period is complete, the fuel will be increased to assist with accelerating the turbine-generator shaft. At approximately 60% speed the torque converter will be "de-pressurized" and the Speedtronic will use fuel control to complete acceleration to FSNL.
The above describes the typical starting sequence for many GE-design heavy duty Frame 9E gas turbines with adjustable torque converters (Torque Adjusters). There are some Torque Adjusters which have three settings (firing; purge; accelerate) and some which have only two (firing; accelerate). (The ones with three settings will have a limit switch input to the Speedtronic, usually 33TM-5, driving L33TM5P; those with only two positions will not typically have this input.) But, the basic operation is still similar to what's described above: purge at a high speed, decelerate to below minimum firing speed drop-out level; slowly accelerate back through minimum firing speed at which time fuel will be admitted and spark plugs will be energized; once flame is detected fuel will be cut back and shortly after that the torque adjuster will be pulsed to "maximum"; when the warm-up time is complete the fuel will be increased to assist with acceleration; at 60% TNH the torque converter will be de-pressurized and the Speedtronic will use fuel to complete acceleration to FSNL.
Adjusting the Torque Adjuster limit switches can be a daunting task the first time it's done; but if one has patience and makes notes, it's much easier to perform later. One has to understand how the Torque Adjuster mechanism works, which limit switches serve which purpose, how to change limit switch settings, and how to manually manipulate the mechanism. One very important thing to note is that one should <b>NOT</b> close the torque converter guide vanes with 20TU-1 energized; this can damage the mechanism, so if adjustments are being made with the Starting Motor running one needs to force 20TU-1 to logic "0" while closing the torque converter guide vanes.
One needs to have someone stationed at the operator interface who is familiar with forcing logic, and then someone needs to be at the Torque Adjuster mechanism. Someone also needs to monitor the current drawn by the Starting Motor. So, it really takes three people. It's loud and noisy and hot in the Accessory Compartment, and there is a lot of management pressure to complete the activity quickly.
No; I know of no procedure for adjusting the limit switches properly. And without being able to be on site to review the configuration and demonstrate how to adjust the limit switches it would be futile to try to write one and post it here on control.com.
Lastly, the difference between FSKSU_FI and FSKSU_WU is somewhat large. This may be due to someone increasing the firing FSR because the speed at which you say firing is occurring is higher than it typically should be, and that usually requires more fuel because of the higher air flows at the higher speed. Firing at a speed higher than approximately 10-12% increases the thermal stresses on the hot gas path parts.
I would also estimate that there may be some combustors which lose flame (as evidenced by high exhaust temperature spreads) when fuel is cut back to warm-up. That's just my guess based on past experience with the differentials similar to the one you describe.
This observation about high exhaust temperature spreads during warm-up and acceleration is just that: a personal observation, made without any data, just personal experience. It doesn't mean the unit isn't working properly, it's just an observation. But, any start attempt that results in flame being established is not a proper start, either.
Hope this helps!
You say the unit at your site has an adjustable torque converter (Torque Adjuster). If that is true, then I would say the Torque Adjuster limit switches are *NOT* adjusted properly. I'm making this statement with the following caveat: It is a typical GE-design Frame 9E heavy duty gas turbine with no unusual auxiliaries, fuels, or sequencing.
The Torque Adjustor should be set to "purge" speed position to cause the unit to accelerate to *approximately* 20% speed during starting (the actual speed is irrelevant; it's supposed to be 150-160% of rated starting motor current) for the purge period. Once the purge period is complete, the unit should decelerate to 9.5% speed (actually the speed will dip slightly below 9.5%) and the torque adjuster should be set to "firing" speed, which will slowly accelerate the unit up through 10% speed at which time the fuel stop valve is opened, the fuel is set to firing value, and the spark plugs are energized.
When flame is detected, the fuel is cut back to warm-up value and after a short time delay the Torque Adjuster will be pulsed to "accelerate" position to begin accelerating the turbine-generator shaft. After the warm-up period is complete, the fuel will be increased to assist with accelerating the turbine-generator shaft. At approximately 60% speed the torque converter will be "de-pressurized" and the Speedtronic will use fuel control to complete acceleration to FSNL.
The above describes the typical starting sequence for many GE-design heavy duty Frame 9E gas turbines with adjustable torque converters (Torque Adjusters). There are some Torque Adjusters which have three settings (firing; purge; accelerate) and some which have only two (firing; accelerate). (The ones with three settings will have a limit switch input to the Speedtronic, usually 33TM-5, driving L33TM5P; those with only two positions will not typically have this input.) But, the basic operation is still similar to what's described above: purge at a high speed, decelerate to below minimum firing speed drop-out level; slowly accelerate back through minimum firing speed at which time fuel will be admitted and spark plugs will be energized; once flame is detected fuel will be cut back and shortly after that the torque adjuster will be pulsed to "maximum"; when the warm-up time is complete the fuel will be increased to assist with acceleration; at 60% TNH the torque converter will be de-pressurized and the Speedtronic will use fuel to complete acceleration to FSNL.
Adjusting the Torque Adjuster limit switches can be a daunting task the first time it's done; but if one has patience and makes notes, it's much easier to perform later. One has to understand how the Torque Adjuster mechanism works, which limit switches serve which purpose, how to change limit switch settings, and how to manually manipulate the mechanism. One very important thing to note is that one should <b>NOT</b> close the torque converter guide vanes with 20TU-1 energized; this can damage the mechanism, so if adjustments are being made with the Starting Motor running one needs to force 20TU-1 to logic "0" while closing the torque converter guide vanes.
One needs to have someone stationed at the operator interface who is familiar with forcing logic, and then someone needs to be at the Torque Adjuster mechanism. Someone also needs to monitor the current drawn by the Starting Motor. So, it really takes three people. It's loud and noisy and hot in the Accessory Compartment, and there is a lot of management pressure to complete the activity quickly.
No; I know of no procedure for adjusting the limit switches properly. And without being able to be on site to review the configuration and demonstrate how to adjust the limit switches it would be futile to try to write one and post it here on control.com.
Lastly, the difference between FSKSU_FI and FSKSU_WU is somewhat large. This may be due to someone increasing the firing FSR because the speed at which you say firing is occurring is higher than it typically should be, and that usually requires more fuel because of the higher air flows at the higher speed. Firing at a speed higher than approximately 10-12% increases the thermal stresses on the hot gas path parts.
I would also estimate that there may be some combustors which lose flame (as evidenced by high exhaust temperature spreads) when fuel is cut back to warm-up. That's just my guess based on past experience with the differentials similar to the one you describe.
This observation about high exhaust temperature spreads during warm-up and acceleration is just that: a personal observation, made without any data, just personal experience. It doesn't mean the unit isn't working properly, it's just an observation. But, any start attempt that results in flame being established is not a proper start, either.
Hope this helps!