Noted with thanks.Dear CH Lee,
Well received... I Wil review it and analyse closer according to your original post... Then come back to you with comments /notes...
Cheers
James
Have a pleasant weekend.
Noted with thanks.Dear CH Lee,
Well received... I Wil review it and analyse closer according to your original post... Then come back to you with comments /notes...
Cheers
James
ThanksNoted with thanks.
Have a pleasant weekend.
First questions...Noted with thanks.
Have a pleasant weekend.
Dear James,First questions...
What the meaning of GCAP/GSP... SCR..
TCS/LOR...
Thank you for your reply
James
Dear CH Lee,Dear James,
GCAP - generator control and alarm panel
GSP - generator sunchronizing panel
SCR - Sync. Check relay.
TCS - Trip circuit supervision relay
LOR - lock out relay.
A bit challenging to operate and troubleshoot the problem if working a lone with this system.
2 generator incoming VCB with all metering located 1.5 meter apart, same roll of GSB , generator switchboard.
The GSP, generator synchronizing Panel 3 meters diagonally opposite GSB, the GCAP is located at another coner in the switchroom.
Feel free to ask if you have any further questions.
FYI, recently auto synchronizing functions developed some problems, Permissive & Run mode unable to close VCB. So I have both Load Release Switches closed, both load share in auto position, manually synchronize by observing synchroscope, once VCB is closed, set both mode switches to Run mode, outcome - load swing vigorously.
Few months ago both Run & Permissive mode were working fine, same load swing was observed too.
OKDear James,
GCAP - generator control and alarm panel
GSP - generator sunchronizing panel
SCR - Sync. Check relay.
TCS - Trip circuit supervision relay
LOR - lock out relay.
A bit challenging to operate and troubleshoot the problem if working a lone with this system.
2 generator incoming VCB with all metering located 1.5 meter apart, same roll of GSB , generator switchboard.
The GSP, generator synchronizing Panel 3 meters diagonally opposite GSB, the GCAP is located at another coner in the switchroom.
Feel free to ask if you have any further questions.
FYI, recently auto synchronizing functions developed some problems, Permissive & Run mode unable to close VCB. So I have both Load Release Switches closed, both load share in auto position, manually synchronize by observing synchroscope, once VCB is closed, set both mode switches to Run mode, outcome - load swing vigorously.
Few months ago both Run & Permissive mode were working fine, same load swing was observed too.
Dear CH Lee,Dear James,
GCAP - generator control and alarm panel
GSP - generator sunchronizing panel
SCR - Sync. Check relay.
TCS - Trip circuit supervision relay
LOR - lock out relay.
A bit challenging to operate and troubleshoot the problem if working a lone with this system.
2 generator incoming VCB with all metering located 1.5 meter apart, same roll of GSB , generator switchboard.
The GSP, generator synchronizing Panel 3 meters diagonally opposite GSB, the GCAP is located at another coner in the switchroom.
Feel free to ask if you have any further questions.
FYI, recently auto synchronizing functions developed some problems, Permissive & Run mode unable to close VCB. So I have both Load Release Switches closed, both load share in auto position, manually synchronize by observing synchroscope, once VCB is closed, set both mode switches to Run mode, outcome - load swing vigorously.
Few months ago both Run & Permissive mode were working fine, same load swing was observed too.
Dear James,Dear CH Lee,
Thank you for your reply
These abréviations are slightly différents from conventional power plant.
I still don't know if MLSC "Master Load synchronizer controller is installed..
Can you confirm if it is installed or not..
Regards
James
GSB is referring to another equipment, Generator Switchboard (11KV).Dear CH Lee,
Sometimes you write GSP... Then you write GSB is that a typing error... Or another device.. Please clarify...
Okay by the way there also close/open command for VCB... Shown on drawings.. can you tell me what is the difference between those signals/contacts/commands...Operate PB, unloading and open the breaker.
By the way, have you ever come across leroy Somer AVR model R630?
Dear James,Okay by the way there also close/open command for VCB... Shown on drawings.. can you tell me what is the difference between those signals/contacts/commands...
Is that PB operated only by operator... Please clarify..
As you stated this is PB is for unloawing/opening Generator breaker..
Also YOU DID not tell me. WHaT is the function of L'on network..
Yes I got experience on that type of AVR...
Do the AVRS... working properly.. To know that you definitely need to install.. Woodward toolkit software that's the key for troubleshooting and solve problem at your site....
Will review closer the drawings even some pages/sheets are missing or not shown deliberaly.. Which you could say it from beginning.. So I can understand that you don't want to show them..
But supporting you remotely without more informations would be very difficult...
Cheers
James
Dear CH Lee,Dear James,
If you follow the drawing closely, you would have realize those open/close Switches are for manual operation.
From my understanding, the operator supposed to operate PB when he wants to stop one generator, the system with ramp the load down to a predetermined level, then automatically open the breaker. Honestly speaking, none of us has the opportunity to operate the PB, simply the problems encounted doesn't Permit us to proceed to that stage of operation.
Other drawings are not relevant/of no value for troubleshooting, and bound by data privacy policy in the company as I am hesitant to share
I am lack of experience in DSLC, my wildguess is Lon networks communicate between 2 DSLC, exchange of date for load sharing which was explained in previous post.
I do understand it is difficult to troubleshoot remotely, particularly for someone is not familiar with the system, if it is too troublesome to continue, I am ok to discontinue the post here.
For Leroy Somer AVR Model R630 incorporates a Digital U Pot / P.F. module, I have a question as how to adjust it to have fine voltage trimming, as currently digital input trimmering is pretty coast, during parallel operation, impossible to trim for balancing the reactive power - always overshot.
Digital Pot U / P.F. Module externally can only access P1, pot to adjust speed, no improvement when making adjustment.
Thanks.
Dear CH Lee..Dear James,
Noted with thanks, enjoy your vacation.
Thanks.
Shunt. Alternator has a PMG.What kind of excitation system is used... Is that Shunt/Arep...