Basic DP Calculation - Unfortunately Not Sure
U
Utz
Problem:
Inlet P: 19.7 psia
Outlet P: 17.7 psia
DP: in gauge?
Solution 1:
DP = 19.7 psia - 17.7 psia
= 2 psia
= 2 psia - 14.7 psi atm
= -12.7 psig
Solution 2:
= (19.7 - 14.7) psig - (17.7 - 14.7) psig
= 5 psig - 3 psig
= 2 psig
Which of the above solutions is correct?
The correct answer is the differential pressure is 2 psi, neither gauge nor absolute. Some would call it 2 psid, where the "d" is for differential.
I would go so far as to say that the differential pressure is only properly stated as 2 psid and not as 2 psi.
The absence of the letter g (for gauge pressure) infers that the units are gauge and not differential or absolute.
psi = psig
psi does not equal psia
psi does not equal psid
curt wuollet
I would think neither.
DP = differential pressure no reference to atmosphere
19.7 - 17.7 = 2 psi dp.
cww
Hi there,
This can be a bit confusing so always make sure you use the SAME pressure platform when you do these calculations. Do not change platforms halfway through the calculation.
0 Psia = -14,7 Psi OR 0Psi = 14,7Psia
Using only the absolute pressure platform:
-14,7 Psi + 19,7 Psia = 5 Psi
And,
-14,7 Psi + 17,7 Psia = 3Psi
So,
5-3 = 2Psi
Also
19.7 psia - 17.7 psia = 2Psi
Because,
19,7Psia = (-14,7 Psi + 19,7 Psia = 5 Psi)
And,
17,7Psia = (-14,7 Psi + 17,7 Psia = 3Psi)
So again,
5-3 = 2Psi