I am trying to establish communications between a Control Logix 5000 PLC, which resides on a Profibus DP network and an Endress and Hauser TMT 184 Temperature Transmitter, which resides on a Profibus PA network.
The PLC uses an SST card to connect to the profibus DP network. The DP network is connected to the PA network bu a siemens Link module (IM 157) and a Segment Coupler.
I am using SST Profibus Configuration Version 1.9 to configure the SST Card. The GSD file for the Link Moldule is Dated "02.04.02 V1.5".
The system is coming up and I can see aall the other instruments on the network but I cannot see the TMT 184 from the PLC. Also the SF light is lit on the Link module and the BF 2 light is flashing.
I would appreciate any help possible....